ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,745 Are you busy
166,650 Re: Forum
160,799 Need opinion
Who's Online Now
0 registered members (), 65 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#79702 - 01/13/02 09:13 AM 314.22  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Pg 44 of the nov NECA guide's 314.22 states the 'significance' of the 02' change as...

Installing surface-mounted boxes over existing flush boxes, to make aditions to electrical systems is no longer permitted.
This revision permits surface extensions to be made only from flush-mounted boxes with extension rings.

HUH? What?! [Linked Image]


314.22 Exposed Surface Extensions.
Surface extensions from a flush-mounted box shall be made by mounting and mechanically securing an extension ring over the flush box. Equipment grounding and bonding shall be in accordance with Article 250.
Exception: A surface extension shall be permitted to be made from the cover of a flush-mounted box where the cover is designed so it is unlikely to fall off or be removed if its securing means becomes loose. The wiring method shall be flexible for a length sufficient to permit removal of the cover and provide access to the box interior, and arranged so that any bonding or grounding continuity is independent of the connection between the box and cover.


2017 / 2014 NEC & Related Books and Study Guides

#79703 - 01/13/02 12:55 PM Re: 314.22  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Wow... So what do we do with all those shallow boxes (with the 45º corners) that are imbedded in jenny lynn or brick/block walls?

Regular WireMold Extensions not allowed?

Somebody spell this out for me (darn legalese)...

My supplier still sells lots of those boxes (the 45º cornered kind) regardless of my prompting that they are only legal for phone wire!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#79704 - 01/13/02 01:19 PM Re: 314.22  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
This was 370-22 in the '99.

It is confusing, I question the mag article, which is (pix) basicaly outlawing 4 sq extension rings

Are we to read this into it??


#79705 - 01/13/02 01:52 PM Re: 314.22  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
guys,
This rule is to prohibit the mounting of boxes over existing flush boxes. When you need to add something on over a flush box, this change is only requiring that you use an extension designed for the purpose. The prohibits the installation of boxes (boxes have backs, extensions have openings it the back that match the size of the opening in the flush box) over flush boxes. This is intended to allow access to the wiring in the flush box without having to remove a box installed on top of the flush box.
Don(resqcapt19)


Don(resqcapt19)

#79706 - 01/13/02 02:17 PM Re: 314.22  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Oh... Thanks, Don...

I was freakin' there for a minute!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI


Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7664 MB (Peak: 0.9023 MB) Zlib enabled. Server Time: 2017-03-29 17:11:18 UTC