The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79607 - 01/08/02 07:52 AM Article 250-52
ayrton Offline
Member

Registered: 12/21/01
Posts: 205
Loc: Pa
In the Technical Licensing Studies Work book for passing the State Exam it has a question regarding lightning rods. "Electrical equipment shall be kept how far from a lightning rod before it must be grounded to the rod?"
It than gives you the answer where to look in Article 250-52.
In the NEC 96 code their is no article '52'
It goes from 250-51 - 250-53.
In NEC 2002 their is an Article 250-52, but no mention of the word 'Lightning rod'.
Is this exam question regarding a grounding electrode or lightning rod. I was under the impression that a lightning rod is to protect a structure form a lightning strike. Am I wrong? Any input would be appreciated.

Top
2014 / 2011 NEC & Related Books and Study Guides
#79608 - 01/08/02 08:43 AM Re: Article 250-52
Elzappr Offline
Member

Registered: 12/20/01
Posts: 273
Loc: Oregon
250-46 in the 96 Code.
250-52 & -106 FPN No.2 in the 99 and '02 Code.
Basically 6 feet..or else the lightning will jump from the "air terminal" ground electrode conductor to other ground electrodes or surfaces..increasing likelihood of burning things. Look in the index for "air terminals" (not "lightning rods"). Also, the ground electrodes for the air terminals need to be AT LEAST 6 feet away from other building ground electrode rods in order to effectively and safely dissipate the lightning charge.

Top
#79609 - 01/08/02 10:15 AM Re: Article 250-52
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Note that NFPA 780 (Lightning Protection Code) requires that the lightning protection system grounding electrode system and the electrical system grounding electrode system be bonded together.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top