The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79552 - 01/03/02 05:50 AM 404.8(B) revision - voltage between switches
mlundy Offline
Junior Member

Registered: 01/03/02
Posts: 2
I have been reviewing changes in the 2002 NEC and had a question that I would like to get the Board's input on. Section 404.8(B) notes that if two devices (a snap switch and another device such as a switch or receptacle) are installed in an enclosure and there is greater than 300V potential difference between the adjacent devices, a barrier between the two devices must be installed.

A Code Change book that I was reading then gave an example of a switch (use to switch a 277V lighting circuit) installed next to a 120V receptacle. It indicated that the voltage between the two devices would be greater than 300V (277V + 120V). However if you were to put a voltmeter probe on one of the conductors of the 277V circuit and the other voltmeter lead on a wire from the 120V circuit, the voltmeter would read 0V because the two supplies are isolated from one another. I have read two different "2002 NEC Change" books and they both provide a similar example. What is your take on this?

I could understand that if two, 277V circuits were switched from two switches in one enclosure there would be a potential difference of 480V between the switches assuming that two different phases were used. However I don't interpret 404.8(B) the way that these two Code Change books have.

Top
2014 / 2011 NEC & Related Books and Study Guides
#79553 - 01/03/02 08:15 AM Re: 404.8(B) revision - voltage between switches
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
You will read voltage becuse the systems are not really isolated. They grounded conductors of both systems will be tied together by the grounding system.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#79554 - 01/03/02 10:53 AM Re: 404.8(B) revision - voltage between switches
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
With a common neutral/ground the voltage you get between a 277V hot and a 120V hot will depend upon which phase of each system is present. It will certainly exceed 300V in some combinations.