#79460 - 12/27/01 06:44 PM Grounding
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
Hi,
Is there not an exception in the 1999 NEC that allows #6 copper to be used for the cold water ground on a 200A service?

This is the grounding electrode conductor is it not?

thanks for any replies.
Top
2017 / 2014 NEC & Related Books and Study Guides
#79461 - 12/27/01 08:12 PM Re: Grounding
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The exceptions only apply to made electrodes like ground rods. The metal water pipe always requires a grounding electrode conductor or bonding jumper sized per Table 250-66. See 250-66.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#79462 - 12/27/01 08:56 PM Re: Grounding
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
in the 2002 NEC section 250.66 (A) it appears to allow a #6 to a pipe.

i am missing how to identify the size difference from the ground rod to the water pipe...i always thought these were the same size.

is there a difference between the 99 code and 2002 code regarding this?

thanks
Top
#79463 - 12/27/01 08:58 PM Re: Grounding
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
in the 2002 NEC section 250.66 (A) it appears to allow a #6 to a pipe.

i am forgot how to identify/determine the size difference between the ground rod and to the water pipe...i always thought these were the same size.

is there a difference between the 99 code and 2002 code regarding this?

thanks
Top
#79464 - 12/28/01 05:06 AM Re: Grounding
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Frodo,
The exception is for a driven pipe electrodemade the same as the way you'd drive a ground rod. It's not for a water pipe.
The driven pipe electrode is normally a pretty crummy ground, but if your soil conditions permit, & you can get it below 25 ohms, what the heck.
Top
#79465 - 12/28/01 01:00 PM Re: Grounding
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Scott is right. 250.66 wil not allow the #6 copout on a H20 pipe, because it's seen as the lowest ohmic value, municipal systems being miles long.
Ground rods are all for show, try & get below 25 ohms, and your rod separation may well be 50' or more, Ufer's will someday rule, if we can be tipped off before the concrete dudes* pour
*knarly bunch that they be...
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals