What does this new exception mean? Does it throw out 725.55?
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
2017 / 2014 NEC & Related Books and Study Guides
#79454 - 12/28/01 04:53 AM Re: 725.52(A) Ex. #2
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Being that the circuit is reclassified as a Class 1 circuit, it sure does look like it would invalidate 725.55
Top
#79455 - 12/31/01 08:11 PM Re: 725.52(A) Ex. #2
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
This is an interesting change. I was taught to think that ONE reason for all the efforts to separate class 2 and 3 wiring from class 1 and power wiring was to protect the technician who thinks he is only dealing with 24 volts from inadvertently getting nailed with higher voltages. I guess this change pretty much nullifies that notion. All they must be concerned with is fire, induction, and fire/smoke characteristics of unprotected cabling!
Top
#79456 - 01/01/02 07:31 AM Re: 725.52(A) Ex. #2
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
How can a Class 2 system which was installed by using Class 2 wiring become a Class 1 system just by removing the Class 2 marking on the system?

Would not the system need to be re-wired using 600 volt wiring and Chapter 3 wiring methods as per 725.27(B) ?
Top
#79457 - 01/01/02 07:51 AM Re: 725.52(A) Ex. #2
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Just changing the the wiring method doesn't make a Class 2 system a Class 1 system. I realy have no idea what CMP 16 was trying to do here. If this is applied in the way that it reads, it does away with 725.55 and I don't think that is the intent.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#79458 - 01/01/02 07:52 AM Re: 725.52(A) Ex. #2
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Glenn,

I think the key phrase in this is "installed as Class 1 circuits." This, as you point out, would require the use of an article 300 wiring method.

I can't imagine why someone would want to just go out & change & existing Class 2 or 3 installation, but there are plenty of times in new work where going to Class 1 makes sense.

This issue was posed at an IAEI chapter meeting several years ago (can't remember which chapter & when) & the response was split about evenly.

If the entire installation complies with Class 1 wiring requirements with an article 300 wiring method, I don't see the hazard that would be introduced. When I see an article 300 wiring method, I presume I'm dealing with at least 120 volts. On the other hand, I have seen lighting outlets wired with doorbell wire and telephone wire. What a surprise that would have been for someone if they cut the cable!

Don, sometimes I think the new code books should come with a deck of Tarot cards.

Tom

[This message has been edited by Tom (edited 01-01-2002).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#79459 - 01/01/02 08:26 AM Re: 725.52(A) Ex. #2
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
Maybe the 725.52(A) text and the FPN text should just remove words " reclassified and ".

Now the circuit is being installed as a Class 1 .
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals