#79428 - 12/19/01 12:36 PM Service raceway outside of bldg
tmon Offline
Member
Registered: 07/05/01
Posts: 29
Would a raceway that runs from underground through a wall into a basement (finished floor) then up through the slab into the service equipment be considered outside of the bldg? The raceway is EMT. The floor is finished concrete but not habitable. It is the crawl space under a dining facility.
Top
2017 / 2014 NEC & Related Books and Study Guides
#79429 - 12/19/01 06:22 PM Re: Service raceway outside of bldg
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
If I'm following you correctly, the conduit is exposed when it comes in the building in the basement. To be considered outside, a 2" concrete encasement must be complete with no breaks.
Does this pertain to location of service disconnect being as near as practical to the entry into the building?

[This message has been edited by Redsy (edited 12-19-2001).]
Top
#79430 - 12/20/01 07:51 AM Re: Service raceway outside of bldg
tmon Offline
Member
Registered: 07/05/01
Posts: 29
Redsy,
Yes it is in reference to that topic.
Top
#79431 - 12/20/01 11:07 AM Re: Service raceway outside of bldg
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
tmon,
Have you looked at Articles 230.70(A)(1) & 230.6? What is the length of raceway that is exposed from the point of entry into the basement to the disconnecting means?

[This message has been edited by Redsy (edited 12-20-2001).]
Top
#79432 - 12/21/01 10:36 AM Re: Service raceway outside of bldg
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
It appears from your post that the conduit is for physical protection of the cable as it passes through the concrete floor slab, thence up to the Servic Entrance Disconnect Switch. This would comply with Art. 300-4 and 300-5(d). However, EMT is not listed as one of the protective means and should not be used in this application.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals