The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
1 registered (annemarie1), 302 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79386 - 12/17/01 01:49 PM 15 or 20 Amp Dilemma?

Recently ran into a dilemma with regards to the proper breaker on a circuit. The simple branch circuit contains a 12-2 w/g feed that has a 14-3 w/g branch from into. Thus creating two circuits from the single 12-2 wire. The debate among elder electricains (who know the code quite well) and inspectors is whether or not the the circuit is to be protected with a 20 amp or a 30 amp fuse. First inclination is that you default to your weakest link and install the 15 amp breaker to protect the 14 gauge wire. However, inspectors in the business for years and some local electricians feel that the circuit can be protected by the 20 amp breaker and meet code. I remember looking this up in the 1996 NEC code and finding support for this. Does anyone have any idea about this? Joe?

2014 / 2011 NEC & Related Books and Study Guides
#79387 - 12/17/01 02:16 PM Re: 15 or 20 Amp Dilemma?
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
See the *Note under Table 310-16 and Section 240-3. See also Section 110-14(c).
Joe Tedesco, NEC Consultant

#79388 - 12/17/01 05:02 PM Re: 15 or 20 Amp Dilemma?
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
15 amp protection. This is similar to installing 15 amp branch ckt. wiring and using #12 for the homerun. It is a 15 amp ckt.