The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#79323 - 12/14/01 06:36 PM Washer in bathroom
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Is there anything in the NEC to prevent the installation of a washing machine in a bathroom?

I'm assuming that the room is big enough to get a suitable distance from the tub, and I also assume that under the current NEC the recept. would have to be GFI protected.

Top
2014 / 2011 NEC & Related Books and Study Guides
#79324 - 12/14/01 06:55 PM Re: Washer in bathroom
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Many apartments have Washer-Dryer combinations in the bathroom. Usually in a nook behind a bi-fold door, though.

Top
#79325 - 12/15/01 01:46 AM Re: Washer in bathroom
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Thanks. The reason I asked is that it seems to be quite common on the Continent, particularly in Spain, but not here in England.

There's nothing against it here in the IEE Regs., so long as the 6' spacing from the tub can be achieved. It would also have to be hard-wired. I've never seen it done here though.

Top
#79326 - 12/15/01 02:25 AM Re: Washer in bathroom
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Electrically,
here it would be a 'dedicated receptacle' and therefore not GFI. I'm not sure how the spacing, as being next to a basin and/or bath, would affect this.

Practically,
I had one customer, washer in bath, who's agitator was one of those that when up and down, instead of the more common side to side. Given a wet floor, the unit hopped it's way into blocking the door, while yanking it's discharge hose from the standpipe....quite the flood!

Top
#79327 - 12/15/01 07:23 AM Re: Washer in bathroom
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Sparky,
There is no "dedicated receptacle" exception in 210-8(a)(1).
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#79328 - 12/15/01 10:21 AM Re: Washer in bathroom
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
hmm, no there isn't, your right.

and we can't just say 210.11(c)(3)EX either , due to 210.11(C)(2) ?!

Looks like a 20A dedicated GFI in a bathrooom ......

Top
#79329 - 12/15/01 12:27 PM Re: Washer in bathroom
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Sparky,

Kind of a complicated way to go about washing the bathroom floor if you ask me.....

Why a 20A GFI circuit? With no heating element in U.S. machines, surely a 15A would be sufficient?

Top
#79330 - 12/15/01 02:05 PM Re: Washer in bathroom
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Paul,
NEC stipulates a 20A laundry circuit, and if it's in the bath, the 'dedicated' thing we can let fly elsewhere does not here, so GFI it is, and IF it were the sole receptacle on said circuit, it would need to be 20A

Top
#79331 - 12/15/01 02:56 PM Re: Washer in bathroom
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Fair enough. If it's a 20A circuit with one outlet then a 20A recept. makes sense, and if the NEC says 20A laundry circuit then 20A it is. But I wonder why they specify a cct. that will take up to 2400W for a load that at most will be much less than that, even if you take the 120% rule into account.

Actually, does the NEC consider a washer a continuous load for cct. rating?

Top
#79332 - 12/15/01 03:25 PM Re: Washer in bathroom
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Paul,

A Laundry area might also have an Iron being used there that might better justify the 20A circuit.

Bill