The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#79304 - 12/14/01 11:11 AM Unused UF cable
sparkless Offline
Junior Member

Registered: 12/14/01
Posts: 6
Loc: deer park ,ohio
I'm re-grading my parking lot. I may want to install a outdoor lit sign in future. I want to lay conduit with UF cable pulled now but not connected to any services. I just want to trench now while I'm working on my asphalt. Pulling the cable now was easier because of my long run. The local county electical inspectors are giving me a notice of non-conforming work. Am I able by NEC code to lay conduot with unused UF cable and no connections or service hookups? What do I need to do to comply? Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#79305 - 12/14/01 06:32 PM Re: Unused UF cable
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
sparkless,

Welcome!
Did they specify what the violation was?

Bill

Top
#79306 - 12/14/01 06:53 PM Re: Unused UF cable
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
What is the depth & length of the trench and what type of conduit? Why UF as opposed to individual conductors?

Top
#79307 - 12/14/01 07:35 PM Re: Unused UF cable
sparkless Offline
Junior Member

Registered: 12/14/01
Posts: 6
Loc: deer park ,ohio
No NEC reference was made. Report states that empty conduit must be empty.

Depth of trench is 2 feet. Length of trench is approx 150 feet. Conduit is grey PVC 1-1/2 inch. I ran UF rather than bare because My electrician told me to pull UF 12-2 with ground. I did not mention earlier that, that a second defect was that I need to add a junction break to keep 360 degrees or less per run. I think this is unrelated to having unused wire pulled and idle. I am going to cut my one run and add a junction to keep bends less than 360 degrees per run.

Thanks for response.

Top
#79308 - 12/14/01 08:14 PM Re: Unused UF cable
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
There could be some debate on weather or not UF is allowed in conduit. But besides that, will they let you install a properly supported WP box at the end of the run and cap the conductors inside? They are probably worried the wire will be inadvertently energized at some point leaving a serious hazard to the public.

Top
#79309 - 12/15/01 07:19 AM Re: Unused UF cable
sparkless Offline
Junior Member

Registered: 12/14/01
Posts: 6
Loc: deer park ,ohio
I've heard this UF cable within conduit issue from a couple of sources now. Nobody has a specific answer to the issue. One electrician said UF may build up heat within conduit. Another said noway unless circuit is overloaded. I would think if I put coded electrical connections at the ends I would be Ok. I was attempting to avoid unnecessary or temporary solutions and expense.

Top
#79310 - 12/15/01 02:48 PM Re: Unused UF cable
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
It may seem nit-picky, but I think the violation cited regarding UF and/or NM in conduit has to do with securing the cable within the required distances of boxes. The rationale being that if it is in conduit, you can't secure it.

Top
#79311 - 12/15/01 08:53 PM Re: Unused UF cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
But if it is in conduit there is no need to secure it, is there? Yes, I know that the rule says you have to, but the purpose of the rule is to prevent the connections from being damaged if the cable is pulled. The cable is protected from being pulled by the conduit. I really see no reason to turn this installation down, but the easiest way to solve the problem would be to install the conduit with a pull string, and install THWN or XHHW conductors when electricity is need for the future project.
Don(resqcapt19)

[This message has been edited by resqcapt19 (edited 12-15-2001).]
_________________________
Don(resqcapt19)

Top
#79312 - 12/16/01 07:26 AM Re: Unused UF cable
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I agree with you, Don. I can'y see any reason to turn it down, given appropriately installed & sized conduit. I actually read that answer at another website. The response was in regard to a similar question.

Top
#79313 - 12/19/01 05:45 PM Re: Unused UF cable
sparkless Offline
Junior Member

Registered: 12/14/01
Posts: 6
Loc: deer park ,ohio
I just added junction to breakup my run that exceeded 360 degrees of total bends. To accommodate my existing line I ran two 45 bends up at one end and at different angles to clear an obstacle. I added a short straight between the 45 bends. As a result my last up pipe is not perpendicular but off perpendicular by a 15 degree angle. What does the NEC code say? Does the termination conduit out of a two feet trench have to be at a perpendicular? Thanks for reply.

[This message has been edited by sparkless (edited 12-19-2001).]