ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/26/17 06:12 PM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,537 Are you busy
166,260 Re: Forum
160,670 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#79293 - 12/11/01 07:03 AM Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Does an existing fire alarm system that is lacking in current compliance need to be brought up to standards?
I hear this is somewhere in NFPA 72 ( we are still on the '96), but cannot find it.
[Linked Image]


2017 / 2014 NEC & Related Books and Study Guides

#79294 - 12/11/01 07:42 AM Re: Fire Alarm Q  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See NFPA 72, 1999 edition, Section 1-2.3
Unless otherwise noted, it is not intended that the provisions of this document be applied to facilities, equipment, structures, or installations that were existing or approved for construction or installation prior to the effective date of the document.

Exception: Those cases where it is determined by the authority having jurisdiction that the existing situation involves a distinct hazard to life or property.


Joe Tedesco, NEC Consultant

#79295 - 12/11/01 07:00 PM Re: Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Joe,
Would this apply across the board? I have old pre-ADA systems who's horn/strobes would not comply per today


#79296 - 12/11/01 07:59 PM Re: Fire Alarm Q  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Sparky: I would say yes because this rule is in the first chapter and covers "Fundamentals of Fire Alarm Systems"

The exception would have to be enforced by the AHJ. Did you ask the AHJ about your systems? If they still work I would not consider it as a "distinct hazard."

Just an opinion .....


Joe Tedesco, NEC Consultant

#79297 - 12/12/01 06:05 PM Re: Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Understood. I think perhaps the confusion is mine, lost bettween code updates and 'change of use' concerning public buildings. I will ask, my AHJ never seems to tire educating me.

[Linked Image]



Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7654 MB (Peak: 0.9049 MB) Zlib enabled. Server Time: 2017-03-27 02:54:38 UTC