#79224 - 12/07/01 07:10 PM Main Breaker
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Does the code say anywhere that the main breaker for a panel must be in a certain loacation e.g., the top or bottom?

A contractor installed a main for a subpanel in apx. the middle of the panel. Although odd, is this non-compliant?
Top
2017 / 2014 NEC & Related Books and Study Guides
#79225 - 12/08/01 06:34 AM Re: Main Breaker
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Wish I could see a picture of this one. i think you're talking about a back fed breaker? See 408.16(f)

The only other restriction I know of is that the "up" position must be "on". 404.7 & 240.81

Tom

[This message has been edited by Tom (edited 12-08-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#79226 - 12/09/01 07:43 AM Re: Main Breaker
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Some resi services I've seen come from the factory with the main CB mounted in the center of the buss. (GE)
If this is a bolt on CB, or has a fastener holding the main in, it's OK. If it's just a plug in type of CB, it's not.(Sorry, I don't have a codebook today)

[This message has been edited by electure (edited 12-09-2001).]
Top
#79227 - 12/09/01 05:07 PM Re: Main Breaker
WireWrestler Offline
Member
Registered: 10/29/01
Posts: 43
Loc: Northern IL
I have installed three SquareD NQOD panelboards in the last two months. 200 amp single phase, 200 amp three phase, and 400 amp single phase. All of these are either top or bottom feed. The factory sets them up per customer specs but they are field convertible. In the commercial installations where I am using them, I prefer the main breaker on the bottom since most new commercial services here must be underground. I have also seen the center feed type (they were old), but I can't remember the brand.
Top
#79228 - 12/10/01 02:57 PM Re: Main Breaker
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
The code doesn't care except that it has to be "up=on, down=off". This is coming from one who (many many years ago) had to redo an entire panel when he was an apprentice.
Top
#79229 - 12/11/01 03:59 PM Re: Main Breaker
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
This happened in an existing apartment building. There was an MDP with main and feeders to several different basement areas. Each feeder was 200a and fed 5 or 6 metersocket/panels ganged together. From the metersocket feed to the panel was #3's. I made the contractor install the main in each panel due to the tap rule requirements. Yes it was a back fed device, and the contractor installed a bracket so the main could not just be pulled out. But he installed the main in the middle of the buss. It turns on and off horizontally, so I guess it sounds like this is ok.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 99 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals