The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (gfretwell), 244 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79192 - 12/02/01 09:30 AM Artice 700/702
Nick Offline

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Consider this scenario.
A retail establishment has a generator that is classified an emergency system and is in compliance with article 700. It has two breakers mounted to it feeding two separate transfer switches. One transfer switch #1 feeds emergency loads IE; exit lighting and emergency lighting fixtures at 277V. Transfer switch #2 feeds a transformer in another electric room that feeds a 120/208V panel. This panel feeds mostly cash registers but also things like power for security doors, the intercom system, and outlets in the computer room.

Ok the question. Can transfer switch #2 be classified an optional standby system and all related wiring be done per article 702? I’m sure losing the cash registers in a power outage is pretty devastating to the owner but I think it is hardly life threatening.

2014 / 2011 NEC & Related Books and Study Guides
#79193 - 12/03/01 05:09 PM Re: Artice 700/702
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I don't see why not. A quick look at 700-1 & 702-2 pretty well defines what each of these systems are. The last sentence of 702-5 says that the user can determine which loads are to be connected to the standby system.

Take a look at 700-5 (a) & (b) to see how much trouble & expense you'll have to go to.

Few things are harder to put up with than the annoyance of a good example.