The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Potseal 6
Who's Online
0 registered (), 92 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79180 - 11/29/01 08:15 PM 10 ft tap rule
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
From my understanding, with this rule you don't need to fuse the feeders of a sub panel less than 10 ft. There is usually no extra lugs to tap off a main panel, so you have to fuse them with a breaker anyway. Am I thinking right?
(Just thought about the 25ft tap rule, have to look it up).
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2014 / 2011 NEC & Related Books and Study Guides
#79181 - 12/01/01 10:34 AM Re: 10 ft tap rule
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
There are so many variables in this question that it's hard to respond.
{240.21(B)(1)}If you have a conductor to a subpanel less than 10'long, that conductor does not have to be protected at its ampacity. It can be 1/10 of the ampacity of the OCPD that feeds it.
{408.16}The subpanel, however cannot be protected by a larger OCPD than its rating, so it would have to be protected by a main breaker or a OCPD in the main panel if the sub's rated at less than the main panel's OCPD.

Top
#79182 - 12/05/01 06:01 PM Re: 10 ft tap rule
bdaddyc1 Offline
Junior Member

Registered: 12/05/01
Posts: 5
aldav53, they do make panels that have a main breaker at the top for the feeds and have lugs at the botom of the panel to feed a sub panel which is a main lug panel sitting next to the main panel, so in a way the tap is just a continuation of the buss bars