#79073 - 11/26/01 05:36 PM Disconnecting Means vs Lock out
DUBLIN Offline
Member
Registered: 09/23/01
Posts: 19
Loc: Menasha, WI, USA
In a residentual single family dwelling with a (whirlpool/shower/steamroom) enclosure,this is a single combination use module. The whirlpool portion is supplyed by 2 20amp GFCI circuits (both circuits controlled by dead front GFCI devices located near the tub inclosure, the load side being terminated in single 20 amp recepticals to be cord connected to each the pump and inline heater).The steam generator is located in the basement 15 feet from the main service panel (within direct site), this is a 2 pole 20 amp circuit. The steam generator has a built in GFCI control (first one i've ever seen). The question is...Is it permissible to install merely a breaker Lock or would one need to adhear to the code more rigidly and install a disconnecting means(other than the breaker itself)?
_________________________
| )ubli| |
Top
2017 / 2014 NEC & Related Books and Study Guides
#79074 - 11/26/01 07:00 PM Re: Disconnecting Means vs Lock out
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
For which component?
Top
#79075 - 11/27/01 03:03 AM Re: Disconnecting Means vs Lock out
DUBLIN Offline
Member
Registered: 09/23/01
Posts: 19
Loc: Menasha, WI, USA
the steam generator, the whirlpool portion has already met code requirements.
_________________________
| )ubli| |
Top
#79076 - 11/27/01 06:05 AM Re: Disconnecting Means vs Lock out
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
A Breaker Handle Lock would seem to be the minimum to get by.

With a 15 foot separation in the basement between steam generator and breaker, I wonder what the long term possibility is for a partition wall being built that breaks line of sight?

Setting a double pole 20 A snap switch at the steam generator would probably be a more conservative approach.

Al
_________________________
Al Hildenbrand
Top
#79077 - 11/27/01 10:48 AM Re: Disconnecting Means vs Lock out
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Dublin,

Hello, Welcome to ECN
Wouldn't the situation that you already have be code compliant?

Bill
Top
#79078 - 11/27/01 02:10 PM Re: Disconnecting Means vs Lock out
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Whoops!

That was a red monkey (don't think of one!).

Dublin. . .the steam generator is probably only resistive heating of a vessel, no motor, so no local in sight disconnect is required. The branch circuit over current protective device is all the disconnect needed.

Coffee, please.
_________________________
Al Hildenbrand
Top
#79079 - 11/27/01 06:55 PM Re: Disconnecting Means vs Lock out
DUBLIN Offline
Member
Registered: 09/23/01
Posts: 19
Loc: Menasha, WI, USA
Thanks ElectricAl kinda the direction I wasleaning towards. The local informed the contractor that he believed the steam generator would require a disconnect, I wasn't able to confirm a definate code requirement so was about to suggest to the local to allow a breaker lock as this is a common practice in the area for (Well pumps,Ovens and cooktops{not cord and plug connected},subpanels in other areas of the home, and other hardwired appliances and motor loads). I've always felt the ability to lockout such items puts everyone in a much safer working inviroment.

Thanks All for the welcome.
_________________________
| )ubli| |
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 95 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals