The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79048 - 11/20/01 01:26 PM Welding Cable as branch circuit and feeders
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Message from reader:

I am reviewing a reseach laboratory design for an owner in which Schedule 80 PVC conduit, and up to 4/0 AWG welding cables are being specified for feeders and branch circuits to maintain power quality.

The "clean power" source is a 180 kVA rotary UPS on the sixth floor of a lab building serving sensitive equipment on the 4th, and 5th floors. The lab professor is requesting the PVC conduit and welding cabling stating that these wiring methods are European standard and required for maximum power quality in his lab.

I question the wiring methods.

To refute the PVC conduit, I can refer to the IEEE Emerald Book, Chapter 9, "Recommended Materials".

I am unable to locate any Code limitation or other authority that prohibits, or even
discourages welding cable as a grounding conductor.

Can someone offer me any advice?

Best Regards,

Jeffrey M. Leavenworth, P.E.
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#79049 - 11/20/01 02:00 PM Re: Welding Cable as branch circuit and feeders
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
This is a listing violation (110-3(b)). 310-13 might also apply since welding cable does not appear in any of the tables mentiond.

From UL's white book "Welding Cable (ZMAY),
"Welding cable...intended for use in accordance with National Electrical Code Article 630, Part E in the secondary circuits of electric welders." Since this laboratory application doesn't involve welders, this cable would not be allowed.

The finer stranding of welding cables may have something to do with lowering their impedance to high frequency currents, but I've never heard of a welding cable actually being applied in this manner.

Tom

[This message has been edited by Tom (edited 11-20-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#79050 - 11/20/01 04:41 PM Re: Welding Cable as branch circuit and feeders
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Even though it is not code compliant, welding cable is often used for temporary power applications. There are types "W" and "P" listed power cables that have very similar construction as welding cables that can be used on power circuits and be code compliant. I looked into one brand of welding cable and Type "W" power cable a few years ago and found that they we identical in every way except that the welding cable had 25% thicker insulation of the same material as used on the Type "W" power cable. The type "W" power cable was suitable for 600 volt power circuits and the welding cable wasn't according to the listing.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#79051 - 11/21/01 11:55 AM Re: Welding Cable as branch circuit and feeders
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Don,

Did you happen to remember how much more type W would cost versus THHN? Just curious.

Tom

[This message has been edited by Tom (edited 11-21-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#79052 - 11/21/01 12:57 PM Re: Welding Cable as branch circuit and feeders
TWM1 Offline
Junior Member

Registered: 09/21/01
Posts: 3
Loc: Ft Hood, Texas, US
This is not an answer to your question but I would like to comment on the welding cable usage. When doing maintenance type work, this cable is great. The high ampacity, the heavy duty rubberized insulation and the flexibility make this a real asset during temp set ups and emergencies.

Top
#79053 - 11/21/01 01:16 PM Re: Welding Cable as branch circuit and feeders
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Tom,
I don't know what the welding cable costs, but diesel locomotive cable which is also very flexible but has a 2000 volt rated insulation costs about 3 times THWN. I have used diesel locomotive cable a number of times on large DC motors that have 700 volt armatures. The last one I did was 1500 hp and took 16 535.3kcmil diesel locomotive cables. 8 for the plus side and 8 for the negative side. This stuff is almost as flexible as welding cable and is great to work with. While I don't find this cable in the NEC, the manufacturers cut sheets say that it is suitable for 90°C wet or dry, in conduits, ducts, or cable tray.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#79054 - 11/21/01 03:54 PM Re: Welding Cable as branch circuit and feeders
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Type “W” cable is roughly twice the cost of thhn copper. I bought a lot of it last summer for a job and our special “big contractor” discount cost was about $1800 per 1000ft. tack on 10-20% for a non-discounted rate and it’s about double the local home center cost on #4/0 thhn. If I remember correctly it was also 2000V rated.