The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
ghost307 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78978 - 11/14/01 07:27 PM line voltage wall thermostat for baseboard heater
944mike Offline
Junior Member

Registered: 11/14/01
Posts: 2
Loc: Hartford, CT
Hi

I have a question for you guys. Is it legal for a line voltage, programable wall thermostat for 240V baseboard heaters to break only one line? I have been told that this is not legal.

I purchased this commercially available line voltage thermostat, sold by Honeywell, that is rated for 240V ONLY, that only breaks one line of a 220V circuit. This thermostat is available for sale currently at Home Depot. My question is, is this legal for residental installations? if not, how can they be manufacturing and selling this thermostat in the United States???

Top
2017 / 2014 NEC & Related Books and Study Guides
#78979 - 11/15/01 05:44 AM Re: line voltage wall thermostat for baseboard heater
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Mike,
Only the disconnect is required to break both conductors. A thermostat is not required to break both sides of the line. If the thermostat has the word "off" on it, then it is a combination thermostat and disconenct and must then break all hot conductors.
See 424-20.
Don(resqcapt19)