The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
Today at 07:36 PM
ESA Arc flash course
by frank
Today at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 27
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
2 registered (Webmaster, sparkyinak), 0 Guests and 223 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#78911 - 11/08/01 02:50 PM nec2002 250.118
ggardiner Offline
Member

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
Can anyone tell me what are the listed cables with acceptable ground return paths are. As it is referred to in 517.13.
Haven't received my copy of 2002 yet and I have to plan installations for the year year.

Top
2017 / 2014 NEC & Related Books and Study Guides
#78912 - 11/11/01 05:23 AM Re: nec2002 250.118
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
The Code does not list cables as being approved or not. It only (517.13) requires that:
"The metal raceway system, or cable armor, or sheath assembly shall itself qualify as an equipment grounding return path in accordance with 250.118."
The cable's listing is what will determine its acceptability
Although they mention A/C, M/C, & M/I cable, the only one I know of is A/C for your useage.
This is nearly a repeat of the Q you already asked in another section of the BB.
Check there

[This message has been edited by electure (edited 11-11-2001).]

Top
#78913 - 11/11/01 06:04 AM Re: nec2002 250.118
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
2002 NEC 250.118 (11) Type MC cable where listed and identified for grounding in accordance with the following:

a. The combined metallic sheath and grounding conductor of interlocked metal tape type MC cable

b. The metallic sheath or the combined metallic sheath and grounding conductors of the smooth or corrugated tube type MC cable


[This message has been edited by Joe Tedesco (edited 11-11-2001).]
_________________________
Joe Tedesco, NEC Consultant

Top
#78914 - 11/11/01 06:06 AM Re: nec2002 250.118
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
lemme see,
the only real 250.118 change in 02' is 250.118(1)
A copper, aluminum, or copper clad aluminum conductor.......

Top
#78915 - 11/11/01 06:53 AM Re: nec2002 250.118
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Be sure to check with the local AHJ as to what edition of the Code they are using before you incorporate any 2002 changes.
Many of them in my area are still basing everything on the '96 Code!

Top
#78916 - 11/11/01 08:35 AM Re: nec2002 250.118
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
Just so everyone understands, the combined metallic sheath and the grounding conductor of the interlocking armor type MC cable does not meet the requirement in 517.13.
don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#78917 - 11/11/01 12:58 PM Re: nec2002 250.118
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Here is the exact reference from the new 2002 NEC. What part of this is not clear or understood?



And here is what the 2002 NEC says in 250.118 (11) Type MC cable where listed and identified for grounding in accordance with the following:
a. The combined metallic sheath and grounding conductor of interlocked metal tape type MC cable

b. The metallic sheath or the combined metallic sheath and grounding conductors of the smooth or corrugated tube type MC cable




[This message has been edited by Joe Tedesco (edited 11-11-2001).]
_________________________
Joe Tedesco, NEC Consultant

Top
#78918 - 11/11/01 01:17 PM Re: nec2002 250.118
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
My point is that MC cable that is listed as an EGC per 250.118(11)(a) is not suitable for 517.13 installations because the sheath istself does not qualify as an EGC. It only qualifies when combined with the internal grounding conductor, and therefore does not meet the requirements of 517.13.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#78919 - 11/11/01 02:29 PM Re: nec2002 250.118
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Joe,
Do you know a company that has type MC or MI Cable that meets the requirements? (Come on, now!) What part don't you understand?
My concern is that if Mr Gardiner specs a freak, it will be a long lead-time item, and will not be acceptable when his EC gets it.
Use AFC's type AC-HCF (as Nick said) or an approved equal, and you can put it to bed.

Top
#78920 - 11/11/01 03:15 PM Re: nec2002 250.118
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Look here:

http://www.afcweb.com/table2.html
http://www.afcweb.com/fieldhcf.htm

Seems like MC cable is also approved for Fire Alarms.



[This message has been edited by Joe Tedesco (edited 11-11-2001).]
_________________________
Joe Tedesco, NEC Consultant

Top