#78903 - 11/06/01 06:01 PM Grounding Gutters/Downspouts
WiCeltic Offline
Member
Registered: 10/13/01
Posts: 20
Loc: Sheboygan, Wi. USA
Art 426, Exposed deicing and snow-melting equipment there is nothing on how or if the gutters/downspouts on a residential house should be grounded. The cable is listed and the manufacturer says to see instructions, which we couldn't find any mention of how to ground the gutters. Going to call manufacture tomorrow, but wondered if any northern electricians had so insight on this. Thanks again.
Top
2017 / 2014 NEC & Related Books and Study Guides
#78904 - 11/07/01 07:58 AM Re: Grounding Gutters/Downspouts
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
There should be no need to ground the gutters and downspouts because 426-27 requires the heating cable to have an conductive grounded sheath and 426-28 requires ground fault protection of equipment for the heat cable. These provisions should eliminate any need to ground the gutters and downspouts.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 107 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals