The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 69 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78839 - 10/28/01 05:29 AM 210.7.C Multiple Branch Circuits on a Yoke
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
I just found this this morning.

2002 NEC section 210.7 - "Branch Circuit Outlet Requirements." part (C) states:

Where more than one branch circuit supplies more than one receptacle on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those receptacles shall be provided at the panelboard where the branch circuits originated.

Raises a question about how to hook up a dual voltage device like a 15A 125V and 15A 250V set of receptacles on one yoke. Or the pair of neutrals and hots to a standard duplex with the tabs removed, where the hots originate from the same bus.

Al
_________________________
Al Hildenbrand

Top
2017 / 2014 NEC & Related Books and Study Guides
#78840 - 10/28/01 06:16 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
ElectricAL,
Is there a corresponding article in the '99 code? I think this requirement is "all new for 2002". Prior to this, I believe a loophole allowed breakers from the same bus to be left un-tied.
One way to do this from the same bus would be to use minis with a tie.

Top
#78841 - 10/28/01 07:05 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
Redsy,

Looks to me like 210.7.C is new to the 2002 NEC. The passage has a vertical line along its side.

I was into the pleasure of a couple strong cups of coffee yesterday when my engineer side ran amok (beware the dark side) and I came up with the two hots from the same bus idea over in the combo fan thread.

I realized later that the material available from the manufacturer probably limits the building of my idea a bit. I mean, I could built this with safety switches or fuse panels with pull outs that are field connected to the bus, but circuit breakers seem to be a problem. In the few places I've looked, I can't find handle ties that are listed for a single tandem breaker. And what about two 240V circuits to a duplex. . .what kind of handle tie works with two pole breakers?

Al
_________________________
Al Hildenbrand

Top
#78842 - 10/28/01 07:26 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
hmmmm,
a dedicated disco that serves a 4-circuit can?
Al, you got a real corker here!

Top
#78843 - 10/29/01 01:31 PM Re: 210.7.C Multiple Branch Circuits on a Yoke
bordew Offline
Member

Registered: 08/27/01
Posts: 155
Loc: Vienna,Ohio, USA
Al;
From what I was just reading is;
Intent: The intent is to require all ungrounded (hot) circuit conductors terminating on multiple receptacles (duplex) on the same yoke to be disconnected simultaneously regardless of type of occupancy. This rule is intended to prevent persons from unintentionally working on energized circuits that they thought were disconnected. the 99 NEC only required the circuit disconnect to simultaneously interupt the multiwire circuit to multiple receptacles on the same yoke if the receptacle was located in a dwelling unit.
REF, MHE 2002 code changes.