The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 298 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78839 - 10/28/01 05:29 AM 210.7.C Multiple Branch Circuits on a Yoke
ElectricAL Offline

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
I just found this this morning.

2002 NEC section 210.7 - "Branch Circuit Outlet Requirements." part (C) states:

Where more than one branch circuit supplies more than one receptacle on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those receptacles shall be provided at the panelboard where the branch circuits originated.

Raises a question about how to hook up a dual voltage device like a 15A 125V and 15A 250V set of receptacles on one yoke. Or the pair of neutrals and hots to a standard duplex with the tabs removed, where the hots originate from the same bus.

Al Hildenbrand

2014 / 2011 NEC & Related Books and Study Guides
#78840 - 10/28/01 06:16 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Is there a corresponding article in the '99 code? I think this requirement is "all new for 2002". Prior to this, I believe a loophole allowed breakers from the same bus to be left un-tied.
One way to do this from the same bus would be to use minis with a tie.

#78841 - 10/28/01 07:05 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
ElectricAL Offline

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA

Looks to me like 210.7.C is new to the 2002 NEC. The passage has a vertical line along its side.

I was into the pleasure of a couple strong cups of coffee yesterday when my engineer side ran amok (beware the dark side) and I came up with the two hots from the same bus idea over in the combo fan thread.

I realized later that the material available from the manufacturer probably limits the building of my idea a bit. I mean, I could built this with safety switches or fuse panels with pull outs that are field connected to the bus, but circuit breakers seem to be a problem. In the few places I've looked, I can't find handle ties that are listed for a single tandem breaker. And what about two 240V circuits to a duplex. . .what kind of handle tie works with two pole breakers?

Al Hildenbrand

#78842 - 10/28/01 07:26 AM Re: 210.7.C Multiple Branch Circuits on a Yoke
sparky Offline

Registered: 10/18/00
Posts: 5545
a dedicated disco that serves a 4-circuit can?
Al, you got a real corker here!

#78843 - 10/29/01 01:31 PM Re: 210.7.C Multiple Branch Circuits on a Yoke
bordew Offline

Registered: 08/27/01
Posts: 155
Loc: Vienna,Ohio, USA
From what I was just reading is;
Intent: The intent is to require all ungrounded (hot) circuit conductors terminating on multiple receptacles (duplex) on the same yoke to be disconnected simultaneously regardless of type of occupancy. This rule is intended to prevent persons from unintentionally working on energized circuits that they thought were disconnected. the 99 NEC only required the circuit disconnect to simultaneously interupt the multiwire circuit to multiple receptacles on the same yoke if the receptacle was located in a dwelling unit.
REF, MHE 2002 code changes.