The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78833 - 10/27/01 07:31 PM Generator disconnect
lousen Offline
Junior Member

Registered: 07/21/01
Posts: 8
Loc: Bryn Mawr, Pa. U.S.A.
Does generator supply entering bldg. underground require a disconnect in bldg? Gen. is 80 feet from bldg.Gen. load 200kva at 208v.

Top
2014 / 2011 NEC & Related Books and Study Guides
#78834 - 10/28/01 03:20 AM Re: Generator disconnect
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Hi lousen!~
good Q
445.18 requires a disco for a genny, but does not specify where...
225-32, general rule , requires a disco. ex#1 could be applied.
If i'm reading this right (part 2 of 225) it matters if the genny serves the outbuilding or not.
others may clarify this better than I

Top
#78835 - 10/28/01 08:11 AM Re: Generator disconnect
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
As a general rule yes. See 225-31. As Sparky stated Ex #1 in 225-32 could be applied but this would have to be acceptable to the AHJ. I don’t believe many would be inclined to accept this.

Top
#78836 - 10/28/01 03:33 PM Re: Generator disconnect
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Lousen,
can you give us more info here? what is the genny used for? etc..

Top
#78837 - 10/28/01 07:03 PM Re: Generator disconnect
lousen Offline
Junior Member

Registered: 07/21/01
Posts: 8
Loc: Bryn Mawr, Pa. U.S.A.
Gen.set mentioned before supplys single owner nursing home.If I open main service disconnect in basement in a fire emergency, Gen. set kicks in.which means power is back on. Nearest disconnect is at Gen. set-80 feet away.This installation is completed but not inspected.

Top
#78838 - 10/29/01 03:40 AM Re: Generator disconnect
Geno Offline
Member

Registered: 08/27/01
Posts: 16
Loc: Syracuse, NY USA
The answer is yes you do need a disconnect within sight. Check out 700.12(B)(6) in the 2002 NEC.

Top