#78773 - 10/24/01 12:33 AM 3 phase delta  
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
Is there a code reference regarding single phase load on the high leg of 240v 3ph delta?
I was asked to defend my stand and could not quote or find anything in the NEC


2017 / 2014 NEC & Related Books and Study Guides

#78774 - 10/24/01 01:55 AM Re: 3 phase delta  
glenn35  Offline
Member
Joined: Jul 2001
Posts: 40
Are you asking if the single Ø 208-grnd is usable? I have never seen any 240V 4 wire that has used a hi-leg by its self. I suppose its possible but what would it be used for?


#78775 - 10/24/01 06:49 AM Re: 3 phase delta  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
The situation you'd run into with the 208V to Neutral would be that standard 1 pole C/B's would not be rated for the voltage, as they're rated at 120V
If you were to use a C/B with a higher rating (277V), or use a fuse with a 250V rating, then I don't think that there's anything to prohibit it in the Code.


#78776 - 10/24/01 08:51 AM Re: 3 phase delta  
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
Thanks for the replies. I was not as clear as I could have been. I am asking about single phase 240 using the high leg with either 'A' or 'C'. I was aware of the 208 and breaker rating mentioned.
In my area it is an 'understood rule' that only 3ph. goes on the high leg. Transformers and services are sized accordingly. Is it a code issue or just a local thing?


#78777 - 10/24/01 09:31 AM Re: 3 phase delta  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
If you think about it, a three phase load is made up of three single phase loads that work together to make advantage of the 120 degree phasing of the source. Each load of a three phase load, taken by itself, is indistinguishable from a single phase load.

Given that phase B is the high leg, adding 240 volt 2-wire loads to A-B and B-C will shift load off the A-C 120/240 side of the delta.

Nothing in the NEC encourages or discourages this placement of load on a 120/240 volt 4-wire delta.

The first thing I would wonder is what the local PoCo's method is for sizing the transformer(s) that supply phase B, the high leg? Do they put the smallest possible can(s) on the pole?

Al


Al Hildenbrand

#78778 - 10/24/01 09:31 AM Re: 3 phase delta  
therain4  Offline
Member
Joined: Dec 2000
Posts: 38
Dunmore,Pa. U>S.A.
I am not sure if this addresses you're Question specificly, atricle 240-85 mentions breakers with a slash designation 120/240 cannot be used between the high leg and another phase (a-b)you need a breaker with a straight 240v rating.


#78779 - 10/24/01 09:49 AM Re: 3 phase delta  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Since sometimes people take code rules and put them where they don't belong (Ya know, I remember the code sez....) someone may be confusing 455-9 for phase convertors where it says single phase loads are not to be put on the derived phase, but this has nothing to do with delta high legs (which are also getting pretty rare).


#78780 - 10/24/01 09:58 AM Re: 3 phase delta  
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
To ElectricAl
Power Co. sizes 'B' for three phase only.

To therain4
That jogs something in my foggy brain. I remembered it was something indirect. 240 delta is still very common here. Is this uncommon in other areas?


#78781 - 10/24/01 10:20 AM Re: 3 phase delta  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
PoCo here, covers several states, refuses all 120/240 4-wire 3-phase requests since the mid '90s. 120/208 only.

As I understand it, they're trying to shift their generator load balancing down to the consumer.

Is the service you are considering old and has 3-phase load been shed, freeing transformer capacity?


Al Hildenbrand

#78782 - 10/24/01 11:05 AM Re: 3 phase delta  
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
Existing service. Someone has added single phase 240 load to high leg and now I am questioning my understanding.

[This message has been edited by wolfdog (edited 10-24-2001).]


Page 1 of 2 1 2

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.034s Queries: 15 (0.003s) Memory: 0.8141 MB (Peak: 0.9869 MB) Zlib enabled. Server Time: 2017-03-30 08:43:24 UTC