The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (HotLine1), 241 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78643 - 10/09/01 10:46 PM PVC requirements
aldav53 Offline

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I did a job today and somebody had run PVC on the outside of a home so I replaced it with emt. As far as I know PVC is subject to machanical damage and not legal run along outside walls. I couldn't find it in the code book.
The Golden Rule - "The man with the gold makes the rule"

2014 / 2011 NEC & Related Books and Study Guides
#78644 - 10/10/01 04:59 AM Re: PVC requirements
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Article 347 1999 NEC (Art 352, 2002 NEC). Generally speaking, schedule 40 PVC conduit is acceptable outdoors where not subject to physical damage. "Subject to physical damage" is a judgment call. However, schedule 80 PVC is acceptable where subject to physical damage. What did you remove?
EMT is not allowed where subject to "severe" physical damage.
My guess is that "severe" alludes to vehicular damage, or industrial environments. [This message has been edited by Redsy (edited 10-10-2001).]

[This message has been edited by Redsy (edited 10-10-2001).]

#78645 - 10/10/01 09:32 AM Re: PVC requirements
aldav53 Offline

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
It was schedule 40 I removed and replaced it with emt, on the back patio of a home, not subject to severe damage, but still needed mechanical protection. PVC also becomes brittle from sun exposure - especially here in Arizona.
Thanks for reply..
The Golden Rule - "The man with the gold makes the rule"

#78646 - 10/10/01 10:46 AM Re: PVC requirements
Bill Addiss Offline

Registered: 10/07/00
Posts: 4196
Loc: NY, USA

To furthur elaborate on Redsy's answer, If you look at Art 347 ('99NEC)(Rigid Nonmetallic Conduit) it starts off (347-1) with a description and characteristics of the conduit and then follows in 347-2 and 347-3 with the uses permitted and not permitted. This same information is in the NEC for each type of conduit, raceway, etc. (348 is for Emt)

As far as what best to use, that would depend on the situation. I'll bet in Arizona you can get some pretty nasty looking pvc sags! Joe T. had a great picture of that somewhere.

Take care,