#78637 - 10/09/01 04:49 PM Cable bending
tmon Offline
Member
Registered: 07/05/01
Posts: 29
Can anyone direct me to a chart or table that gives some direction on or about low voltage (600v or less) cable bending radii? Thanks, Tom
Top
2017 / 2014 NEC & Related Books and Study Guides
#78638 - 10/09/01 05:11 PM Re: Cable bending
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Tom,

I don't have a list or chart, but you can look in the NEC under each cable type if that helps.

AC - 333-8 5x diameter
MC - 334-11(a)(b)(c)- depends on type
NM - 336-16 5x diameter
SE/USE - 338-6 5x diameter
etc.

Bill
Top
#78639 - 10/09/01 07:19 PM Re: Cable bending
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
This reminds me of a Q that is related...

Let's take #12-2-G NM Cable (Romex) for instance...

336-16 states that bends in NM Cable shall have a radius 5 times the diameter of the cable.

With 12-2-G being flat does this translate to a bending radius of 2-1/2" (5 x 1/2" wide)? The same circumference as a 5" hole saw?!?!?

I don't "square off" my corners, but I don't think I leave quite that large of a "sweep" in the cable around corners either...

Am I reading to much into this again?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#78640 - 10/10/01 05:27 AM Re: Cable bending
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
sparky66wv,
I wouldn't sweat it. What about the conductors connected to the devices in the boxes. They mostly all would violate the radii. Although this is may not technically be "cable". I don't square off corners, either, and am conscious of the radii, but most installations on the side of a stud which goes through a bored hole violate this.
Top
#78641 - 10/11/01 05:14 AM Re: Cable bending
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
A curious question concerning Romex. If you had to run the Romex in conduit, how would you determine the conduit fill? Is the area given on the box (or whatever) when it is purchased? The area can be calculated, but??
I realize Romex is usually not run in conduit, but there may be instances where it could be used.
Top
#78642 - 10/11/01 05:20 AM Re: Cable bending
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Warren,
You have to do your own area calculations for romex using the major dimension for the calculations. See note 9 to Table 1 in Chapter 9.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals