ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
fuse rejectors
by gfretwell. 03/23/17 01:12 PM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
TRUE POWER
by jraef. 03/21/17 09:13 PM
WEG CFW-11 Frequency Inverter
by jraef. 03/21/17 08:50 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,245 Are you busy
165,957 Re: Forum
160,481 Need opinion
Who's Online Now
0 registered members (), 57 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#78608 - 10/06/01 10:26 AM 3ph 200a + 100a + 100a  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
I was looking at a prospective job yesterday and was told by the owner that he was told he had to replace everything with a 400a service. Conductor sizes were fine. The arrangement was an overhead fed meter, to a gutter below, a 100a breaker panel on the right, a 100a disconnect on the left to a subpanel, and a 200a disconnect on the left to a subpanel. The owner thinks the issue had to do with this being 3 phase and feeding the 200a panel. Is there enough information here to guess what might be wrong that would require replacing this with a 400a service, CT can... the whole enchilada?


2017 / 2014 NEC & Related Books and Study Guides

#78609 - 10/06/01 04:35 PM Re: 3ph 200a + 100a + 100a  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
If the subfeeds / subpanels will have increased loads connected to them [like 50% or more of their maximum capacity], plus the loads will be running at the same time ,along with 3 hours or more [LCL], than this new load calculation might very easilly exceed the existing service capacity.

Is the existing service 200 amps?

If this Client plans to draw high loads and expand in the future, the 400 amp service is a valid concern.
Calc the project out, then figure out what is the best way to go.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#78610 - 10/07/01 09:54 PM Re: 3ph 200a + 100a + 100a  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
No, there is not enough information.
Please clarify...
WHO told the owner to replace everything?
What do you mean "the conductor sizes look fine"?
Being 3 phase has no significance.
What is the existing load demand?

[This message has been edited by Redsy (edited 10-07-2001).]


#78611 - 10/08/01 11:50 AM Re: 3ph 200a + 100a + 100a  
WARREN1  Offline
Member
Joined: May 2001
Posts: 176
Greenville, SC, USA
Not enough information. And yes, 3 phase will make a difference for phase load balance, which will be of some concern. We try to keep phases balanced within 10% on the connected load schedules.


#78612 - 10/08/01 08:56 PM Re: 3ph 200a + 100a + 100a  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Warren,
I still don't understand why it being a 3 phase service has any bearing on whether an upgrade is needed. I think the main concern is load calculations. The panel layout may be a matter of convenience.



Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7663 MB (Peak: 0.9042 MB) Zlib enabled. Server Time: 2017-03-23 22:08:32 UTC