#78608 - 10/06/01 07:26 AM 3ph 200a + 100a + 100a
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
I was looking at a prospective job yesterday and was told by the owner that he was told he had to replace everything with a 400a service. Conductor sizes were fine. The arrangement was an overhead fed meter, to a gutter below, a 100a breaker panel on the right, a 100a disconnect on the left to a subpanel, and a 200a disconnect on the left to a subpanel. The owner thinks the issue had to do with this being 3 phase and feeding the 200a panel. Is there enough information here to guess what might be wrong that would require replacing this with a 400a service, CT can... the whole enchilada?
Top
2017 / 2014 NEC & Related Books and Study Guides
#78609 - 10/06/01 01:35 PM Re: 3ph 200a + 100a + 100a
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
If the subfeeds / subpanels will have increased loads connected to them [like 50% or more of their maximum capacity], plus the loads will be running at the same time ,along with 3 hours or more [LCL], than this new load calculation might very easilly exceed the existing service capacity.

Is the existing service 200 amps?

If this Client plans to draw high loads and expand in the future, the 400 amp service is a valid concern.
Calc the project out, then figure out what is the best way to go.

Scott SET
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#78610 - 10/07/01 06:54 PM Re: 3ph 200a + 100a + 100a
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
No, there is not enough information.
Please clarify...
WHO told the owner to replace everything?
What do you mean "the conductor sizes look fine"?
Being 3 phase has no significance.
What is the existing load demand?

[This message has been edited by Redsy (edited 10-07-2001).]
Top
#78611 - 10/08/01 08:50 AM Re: 3ph 200a + 100a + 100a
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
Not enough information. And yes, 3 phase will make a difference for phase load balance, which will be of some concern. We try to keep phases balanced within 10% on the connected load schedules.
Top
#78612 - 10/08/01 05:56 PM Re: 3ph 200a + 100a + 100a
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Warren,
I still don't understand why it being a 3 phase service has any bearing on whether an upgrade is needed. I think the main concern is load calculations. The panel layout may be a matter of convenience.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals