The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#7858 - 02/26/02 06:16 PM Outlet in Garage for Table Saw
Phil Offline
Junior Member

Registered: 02/26/02
Posts: 1
On a 30 amp circuit (10/3 romex and 30 amp breaker), supplying a single outlet in a garage (for a table saw), can a 15 or 20 amp receptacle be used (to match the 15 amp 220 volt plug on the saw), or must it be rated to the full current rating of the circuit, i.e., 30 amp receptacle?

Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#7859 - 02/26/02 07:25 PM Re: Outlet in Garage for Table Saw
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#7860 - 02/26/02 08:09 PM Re: Outlet in Garage for Table Saw
beach Offline
Member

Registered: 02/12/02
Posts: 26
You can remove the 30 amp breaker, install a 20 amp, keep the wiring and install a 20 amp receptacle (look for a commercial back wire that will accept 10 awg).

Jon

Top
#7861 - 02/27/02 08:20 AM Re: Outlet in Garage for Table Saw
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
In addition to this, Table 210.21(B)(3) requires a 30 amp receptacle on a 30 amp ckt. regardless of how many receptacles are installed.