The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by sparky
58 minutes 49 seconds ago
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#7853 - 02/23/02 08:18 PM Is this panel proper???
Tom Post Offline

Registered: 09/28/01
Posts: 11
Loc: Philly
In a 4 unit building. The meter bay has 7o amp breakers from each meter that supplies a 60 amp breakers via #2 alum. the 60 amp goes to the main panel inside each unit via #4 alum. All are done inside metal conduit. All of the main panels inside the apartments have the nuetrals isolated from the grounds, however the grounds are attached to the condiut and not the panel. Two of the panels had a bond lug to the inside of the panel that were attached to the nuetral bus. The other two panels were not bonded to the nuetral. What am I missing here? Furthermore, the apartments are all electric baseboard heat. They are very small 1 br apartments but this just seems like 60 amp supply is insufficient. Am I wrong?
Thanks, Tom

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#7854 - 02/24/02 09:37 PM Re: Is this panel proper???
Dorsey K. Jones Offline
Junior Member

Registered: 02/25/02
Posts: 1
Tom, The #2 is ok and so is the #4. The way I read your post tells me that the apartments are only recieving 60 amp. Sounds like you need to upgrade if your heat is bb's. As for the "bond lug" that was attached to the "nuetral bus". That's improper. The ground wires are attached to the "metal conduit". If you look I am sure that you will find the "metal conduit" is attached to the panel. Hence, if your "bond lug" is attached to the "nuetral bus" you are no longer isolating the nuetral and ground.

#7855 - 02/25/02 05:00 PM Re: Is this panel proper???
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Well, you could try doing a load calculation for the feeders, just follow the examples in the back of the NEC. If the breakers haven't been tripping & the connections don't show signs of overheating, you might let this sleeping dog lie, especially if the load calc works out.

Few things are harder to put up with than the annoyance of a good example.