#78527 - 10/02/01 01:08 PM sub panel grounding
ken m Offline
Member
Registered: 08/14/01
Posts: 58
Loc: south carolina
i know this is a particularly worn out question. however, would someone please tell me the code book location that pertains to why a 4 wire feeder is needed for a sub panel that is fed either from the load side of the meter or is fed from a breaker located within the main panel? the local inspectors are looking for backup (reference) when the meter box and the main panel are not located back-to-back and a 4 wire is needed. thx for any help. ken m
Top
2017 / 2014 NEC & Related Books and Study Guides
#78528 - 10/02/01 01:37 PM Re: sub panel grounding
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
250-24(a)(5)
"LOAD SIDE GROUNDING CONNECTIONS. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article."
This is assuming your Main Bonding Jumper is located in the meter enclosure.
Top
#78529 - 10/02/01 02:02 PM Re: sub panel grounding
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Nick,
It has nothing to do with the location of the main bonding jumper. If there is no service disconnect between the meter and the panel a 4 wire conenction is not required. The grounded conductor can be used to bond anything on the line side of the service disconenct and within the service disconnect enclosure. The 4 wire feeders are only required on the load side of the service disconnecting means.

Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#78530 - 10/02/01 02:19 PM Re: sub panel grounding
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Your right!
Top
#78531 - 10/02/01 04:25 PM Re: sub panel grounding
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
See Section 384-20 for the refrence that includes the answer to the question. The NECH also gives a good explanation as to the reason for the isolated neutral in that sub panel.
_________________________
Joe Tedesco, NEC Consultant
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals