The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
2 registered (Admin, dougwells), 73 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78519 - 10/01/01 08:18 AM 10 foot tap rule
NBuc100101@peoplepc.com Offline
Junior Member

Registered: 10/01/01
Posts: 2
Loc: West Seneca, NY
We have a main breaker in an electrical enclosure (300 A). We come off of the top of the breaker to a 30 A breaker in the same enclosure. This is within ten feet. Can we go to field devices outside the enclosure off of the load side of the 30 A breaker?

Top
2017 / 2014 NEC & Related Books and Study Guides
#78520 - 10/01/01 10:20 AM Re: 10 foot tap rule
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
You can go anywhere you want off the load side of the 30 amp breaker as long as you use 30 amp wire. If by "come off the top of the breaker", you mean that you have landed the tap wires in the same terminal as the feeder conductors, you have a violation unless the terminals are listed for those two conductors.
Don(resqcapt19)
_________________________
Don(resqcapt19)