The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78432 - 09/23/01 09:28 PM Conductors in Parallel
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Subject:
Question
Date:
Sun, 23 Sep 2001 16:47:20 -1000
From:
"Joe Wilhelm"
To:



Hello,

I would appreciate your help with the following:

If I understand correctly, a 14 gauge wire is rated for 15 amps and 8 gauge
is rated for 40 amps. If I combine the 14 and 8 wires in parallel does that
then provide 55 amp load capability?

Thank you.

This installation is contrary to common practice. Please see Sections 110-8 and 310-4 in the 1999 NEC.
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#78433 - 09/24/01 03:41 AM Re: Conductors in Parallel
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
me thinks the #14 would be in trouble

Top
#78434 - 09/24/01 04:29 AM Re: Conductors in Parallel
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
First off 310-4 only permits conductors 1/0 and larger to be paralleled. It also requires they be the same diameter.
Secondly, the values suggested for ampacity are ambiguous, due to lack of conductor & application detail.

Top
#78435 - 09/24/01 07:01 AM Re: Conductors in Parallel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
While this installation is not code compliant, neither conductor would be overloaded. If you use the AC resistance from Chapter 9 Table 9 you can solve this as parallel resisitor problem. If we make the circuit 100' long and assume a 55 amp load the resistnace of #14 is 0.31 ohms and the the #8 is 0.078 ohms. The total resistance of these two conductors in parallel is:

1/0.31 + 1/0.078 = 1/Rt = 16.046

Rt= total resistance

1/16.046 = 0.0623 ohms = resistance of 100' of #14 in parallel with 100' of #8

Now if we use E=I(R) to solve for the voltage drop we get E= 55(0.0623) = 3.426 volts

We can now use this voltage drop to solve for the current in each of our conductors.
Again E = I(R) 3.426 = I(0.31) = 11.05 amps for the #14.

3.426 = I(0.078) = 43.92 amps for the #8

These two values do not exactaly equal 55 amps due to rounding. They do total 54.97 amps.

Don(resqcapt19)

[This message has been edited by resqcapt19 (edited 09-24-2001).]
_________________________
Don(resqcapt19)

Top
#78436 - 09/24/01 01:04 PM Re: Conductors in Parallel
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Subject:
RE: Follow-up to Answers to your question
Date:
Mon, 24 Sep 2001 10:11:25 -1000
From:
"Joe Wilhelm"
To:
"Joe Tedesco"


Joe, Thank you very much for your help! While I get around on the internet,
I don't know how to "post" or put up a reply or follow-up question... so if
I could ask you to please post this follow-up:

Thank you all for your helpful comments, especially "resqcapt19" for your
calculations! In light the reply's, could you please tell me how much
current 8 gauge will carry at 220V and 110V over a 50' long run? I'm
thinking of using a 50 amp double pole breaker (220V) by the main panel to
feed the 220V to another box 50' away with 4 number 8 wires (2 hot, 1
neutral, 1 green). The box at the end of the 50' will have at least 1 double
pole 20 amp breaker for a 220V line and some 20/15 amp breakers for 110V
lines. Will this work ok? Would it meet "code"? Someone told me that a
number 8 wire is only good for 40 amps so that's why I was thinking of
combining the 8 and 14 wires (a 3/4" conduit is already in place and I don't
think I can get 4 number 6 wires through it). Thank you all for your help!
_________________________
Joe Tedesco, NEC Consultant

Top
#78437 - 09/24/01 01:43 PM Re: Conductors in Parallel
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Joe,

It's quite easy to post a reply here. You just have to register first. You just fill out a simple form where you choose a "Name" and a password. Then you only have to click on "Post Reply" to respond to something already here or "Post New Topic" will start a totally new Topic.

BTW, If I'm not mistaken, according to table 250-122 you could run a #10 for your ground. That would be 3 #6 and a #10 in your 3/4" conduit for the 50A circuit.

Bill

Top
#78438 - 09/24/01 02:05 PM Re: Conductors in Parallel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
The #8 is limited to 40 amps unless the terminations at both ends of the wire and the wire itself is listed for 75°C. Four #6 THWN will fit in a 3/4" conduit. Also Table 250-122 only requires a #10 ground wire for a 40 or 50 amp circuit. You could install three #6 and one #10 to make the pull a little easier. The voltage drop on a 120 volt circuit of #8 50' long with 40 amps of load would be 3 volts of 2.5%.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#78439 - 09/24/01 04:39 PM Re: Conductors in Parallel
jw Offline
Junior Member

Registered: 09/24/01
Posts: 1
So the voltage drop of #8 for 50' is 3 volts... what is the resistance of 50' of #8?

Top
#78440 - 09/24/01 06:21 PM Re: Conductors in Parallel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
jw,
I used a voltage drop calculator on another site to figure the voltage drop. I didn't use the resistance, but it would 0.039 ohms.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top