The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 139 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78426 - 09/22/01 08:13 PM Re: Working Clearance for HVAC Equip
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
From the 'Mailbag'
 Quote:
I have installed a 7 1/2 ton split system air conditioning unit in an electrical/communication room. It is 460 V 3 phase. According to the UMC I need to have a 30" X 30" clear access for where the power is tied into the unit and for controls. I have an inspector who is saying that I must go by the NEC and have 30" X 42" clear access, due to the voltage. Can you help me out.
Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#78427 - 09/23/01 07:53 AM Re: Re: Working Clearance for HVAC Equip
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Your inspector is correct if you have a grounded surface on the opposite side of the workspace.
NEC 110-16 deals with working clearances.
Table 110-16(a) gives the working clearances as they apply do different situations.
At 151-600V to ground, the clearances are:
1)No live or grounded parts on other side=3'
2)Grounded parts on the other side=3-1/2'
3)Live parts on both sides=4'

In any case, the 30" in the UMC is not sufficient by NEC, as the requirement at 0-150V is 3' in any of the conditions mentioned above.