The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 252 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78426 - 09/22/01 08:13 PM Re: Working Clearance for HVAC Equip
Bill Addiss Offline

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
From the 'Mailbag'
I have installed a 7 1/2 ton split system air conditioning unit in an electrical/communication room. It is 460 V 3 phase. According to the UMC I need to have a 30" X 30" clear access for where the power is tied into the unit and for controls. I have an inspector who is saying that I must go by the NEC and have 30" X 42" clear access, due to the voltage. Can you help me out.

2014 / 2011 NEC & Related Books and Study Guides
#78427 - 09/23/01 07:53 AM Re: Re: Working Clearance for HVAC Equip
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Your inspector is correct if you have a grounded surface on the opposite side of the workspace.
NEC 110-16 deals with working clearances.
Table 110-16(a) gives the working clearances as they apply do different situations.
At 151-600V to ground, the clearances are:
1)No live or grounded parts on other side=3'
2)Grounded parts on the other side=3-1/2'
3)Live parts on both sides=4'

In any case, the 30" in the UMC is not sufficient by NEC, as the requirement at 0-150V is 3' in any of the conditions mentioned above.