#78400 - 09/19/01 05:19 PM GEC Termination
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#78401 - 09/19/01 05:40 PM Re: GEC Termination
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I have 'run-thru' GEC's using siemens LK-2's on strips, no problem whatsoever.
Top
#78402 - 09/20/01 05:29 AM Re: GEC Termination
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The problem I've had with this has stemmed from the head of the screw that fastens the lug to the enclosure protruding into the path of the conductor. I tried flat head screws, but had to chamfer the hole in the lug to accommodate the screw's bevel (then thought I was probably voiding said lug's listing...no help)

Any more, I just use a 2 conductor lug, and be done with it.
Top
#78403 - 09/21/01 07:55 AM Re: GEC Termination
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
Quote:
Originally posted by Nick:
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is [b]does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?[/B]


Just substitute a listed lay in lug. These are open on one side to permit the insertion of the conductor without needing to feed it through. They have a forked opening in the end opposite the mounting hole.
--
Tom
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#78404 - 09/24/01 06:41 PM Re: GEC Termination
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
That's a great solve!
Top
#78405 - 10/18/01 04:07 PM Re: GEC Termination
gary long Offline
Member
Registered: 02/20/01
Posts: 32
Loc: Greeley,Colorado,USA
Dont forget to take a wire brush and scrape that paint off under and around the lug first !!
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 46 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals