The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by JHellingElectric
Today at 07:02 PM
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (JHellingElectric), 238 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78363 - 09/11/01 04:08 AM Neutral Fault Test
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
In one of our municipalities, city code requires that a torque test be performed in front of the inspector (all panel and EXO terminations). OK, no biggy.

The same city requires a neutral to ground fault test. The building ground is disconnected from the neutral connection, and a test for continuity from load neutral to ground is performed. Kind of a pain in the ***, but it seems like a good idea.

Anybody else ever run into this? It's a first for me.

2014 / 2011 NEC & Related Books and Study Guides
#78364 - 09/11/01 04:27 AM Re: Neutral Fault Test
sparky Offline

Registered: 10/18/00
Posts: 5545
??what is, or how is it tested?, i'm drawin' a blank here Scott......

#78365 - 09/11/01 04:47 AM Re: Neutral Fault Test
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA

#78366 - 09/11/01 05:07 AM Re: Neutral Fault Test
Nick Offline

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
This wouldn't be Huntington Beach would it?!

#78367 - 09/12/01 05:04 AM Re: Neutral Fault Test
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Right-ee-o, Surf City USA. Is this the only place where this is done? I'll add some more of their oddities for the other guys.
1.Appliances hardwired (GD, DW, etc). Disco means mounted where you'd normally put your recp.
2.PVC outdoors(or EMT, GRC painted with $60 per gallon marine paint) Go down the street a couple of blocks to Newport Beach, and they'll lynch you for using PVC on the roof.
3. 2x4 fluorescents in T-bar, 4 support wires to structure, 4 screws to grid. Downlights in T-bar 2 wires to structure, 4 screws.

The process is to remove the grounding connection from the service neutral (I had a hot service, so was allowed to remove the neutral feeder conductors from their lugs in the panels, on a resi service, you take all the branch circuit neuts off and test them individually)
A continuity check is then taken from the neutral bar (or branch circ cond) to ground. You shouldn't have continuity. If you do, there is a fault someplace (screw through cable, etc). It would show up on an ungrounded conductor by a tripped C/B, but on a neutral, would never be found without this test. Seems like a real good idea to me.
I just have never heard of it elsewhere
(HB once had an inspector that thought "outside the box")

#78368 - 09/12/01 01:17 PM Re: Neutral Fault Test
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
I hadn't really thought about this before, but with your common neutral/ground busbar, I guess to find a short on a branch circuit you would have to test before both are connected to the bar.

In the U.K., we always have separate neutral and ground busbars, even in places where PME is used and the ground is bonded to the incoming neutral.

It's standard practice on a new installation to do two final megger tests:

1. All switches closed, bulbs removed, appliances unplugged etc. Test between hot & neutral with all fuses in/breakers closed.

2. Temporarily strap hot to neutral and megger between them and the ground busbar. It's also acceptable to do two separate tests: hot to ground & neutral to ground.

We don't even need to disconnect any main cables for these tests on domestic work, because our main switches are D.P. and open the neutral as well.

#78369 - 09/12/01 07:47 PM Re: Neutral Fault Test
Nick Offline

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Originally posted by electure:
Right-ee-o, Surf City USA. Is this the only place where this is done?

This is the only place I know of. I have never worked there but have heard all the complaining of co-workers that have. We do a lot of work there especially at Bowing. I think the neutral to ground test is a good idea. They do get a little carried away sometimes. One example: Parallel conductors. My superintendent was called by a Huntington Beach inspector because the CONDUITSwere not the same length. They knew the city was very particular about having the conductors exactly the same length(absolutely no variance) so they laid them on the floor, cut them EXACTLY the same length and then installed them without cutting them. The inspector would not pass the installation because the conduits were different lengths.

#78370 - 09/12/01 11:31 PM Re: Neutral Fault Test
Scott35 Offline

Broom Pusher and

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I also had the test done in Huntington Beach, along with a few other areas. John Childress from Simi Valley DBS is one that prefers this test.
It's a great idea to check it after the other trades have finished, just to make sure there's no re-grounded grounded conductors! [what a redundant statement ].
Not only that, but the "Neutral Disconnect Link" which service type switch gear has, gets to be used finally!

One other thing about Huntington Beach was penetration of the methane barrier under concrete slabs. I guess that there's an increasing amount of methane gas being pushed inland from the ocean. There's sure a lot of oil pumps in that area!!!

We saw cutted the existing slab to install floor boxes and stubs for teller line [bank branch project] and the Building Department was very concerned with us penetrating the methane barrier.

FYI: The SCE feeder conduits, along with the Telco riser duct to the MPOE were sealed like a gas station's conduits would be. Very rarely see that done!

Scott [electure],
We had to paint the heck out of any underground/underfloor ducts, conduits and boxes too! Once again, the methane situation must be the reason for this.
The Fire Sprinkler's feed [from street to the PIV inside building] was also required to be painted this way.
Wonder if the Landscapers' had to treat their irrigation lines??? - It's possible! I could see methane being able to penetrate the PVC, then enter the irrigation lines and concentrate.

There's a few other AHJ's that want Disposals, Dishwashers, and the like to be hardwired [flex whips]. City / County of LA is one, and I think that Azusa does too. Seems that San Diego is another.

Scott SET
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#78371 - 09/13/01 06:45 PM Re: Neutral Fault Test
sparkie Offline
Junior Member

Registered: 06/27/01
Posts: 7
Loc: mad river, ca usa
I had a Calif State Mobile Home inspector do this on a mobile I replaced the subpanel in. It showed continuity between the N & G. On further investigation the water heater had the N & G tied together.

#78372 - 09/14/01 03:41 PM Re: Neutral Fault Test
sparky Offline

Registered: 10/18/00
Posts: 5545
!!DING !! okay i got it, thanks

come to think of it, not a bad idea for any power quailty concerns either....