#78336 - 09/10/01 01:35 PM Temporary Generator
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
305-6(a), Exception No.1. What is the reasoning
for this exception? I know it's been in there for years. How can you tell if
you meet this exception? I know the obvious if its over 5 kw but say you got
a 4500 watt generator (which are common), how do you know if you meet this?
I was told one way if you have dual voltage 120/240 then you would not meet
that exception. Is that dual voltage reasoning (if true at all) because if
you had 240, you would have 2 hot wires and one neutral thus equal 3 wires?


[This message has been edited by Joe Tedesco (edited 09-10-2001).]
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#78337 - 09/10/01 04:09 PM Re: Temporary Generator
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
Even if it is only a 2 wire generator, you can't use the exception. 250-20(b) requires the system to be a grounded system. There is nothing in 305 that says it doesn't have to be a grounded system and if it is grounded, then GFCI protection is required. If its not grounded, it is a violation of 250-20(b).
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#78338 - 09/10/01 04:14 PM Re: Temporary Generator
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
Joe, i think they mean the 120V receptacles on the 5kw and less units, regardless of other features.
I'll bet this exception was lobbied by the makers of generators.
Top
#78339 - 09/11/01 08:49 AM Re: Temporary Generator
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Thanks for your replies. I expect that the person who asked this question will join in soon, I hope.

Joe
_________________________
Joe Tedesco, NEC Consultant
Top
#78340 - 09/11/01 07:11 PM Re: Temporary Generator
buddy Offline
Member
Registered: 09/11/01
Posts: 11
I posted the question to the board and don't really agree with the responses and here's why. I don't think the generator has to be grounded and if it was, then what requires GFCI protection? That is what the exception is all about, not requiring GFCI's. What I basically want to figure out is how is an inspector supposed to know if a generator meets that exception? Thanks
Top
#78341 - 09/12/01 06:03 AM Re: Temporary Generator
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Buddy,
In my opinion, this exception could be used if you verify that there is not a bond between the frame of the generator and a circuit conductor. The exception also requires that it only be a 2 wire generator, which would preclude the use of a 120/240 volt generator. Are there any portable generators currently available that do not have a conductor bonded to the frame? I've never seen one without this bond.

Is a portable generator a separately derived system?

Don(rsqcapt19)
_________________________
Don(resqcapt19)
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 99 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals