#78128 - 08/21/01 10:25 AM Stove outlet
Todd Offline
Junior Member
Registered: 08/21/01
Posts: 3
Loc: Cincinnati, Oh USA
I just purchased a new Kenmore oven and the manual calls for a minimum of 8 Gauge solid copper on a 40 Amp circuit. I went to Home Depot and purchased 60 ft. of 8-3 with ground. When I got home I noticed that it is NOT solid copper but stranded copper. Will this matter? the manual specifically calls for solid. should I worry about it or is it ok since it will be on a 40 Amp breaker?

Just bought the place and don't want to burn it down! (wife would be angry) Thanks.
Top
2017 / 2014 NEC & Related Books and Study Guides
#78129 - 08/21/01 01:36 PM Re: Stove outlet
Anonymous
Unregistered

You probably should have gotten 60' of 6-3-G (because of distance if your wife cooks much). Stranded wire is fine. Solid copper is more difficult to work with.


[This message has been edited by Dspark (edited 08-21-2001).]
Top
#78130 - 08/21/01 01:38 PM Re: Stove outlet
Anonymous
Unregistered

Your wire is solid copper in the sense that it is not copper-clad aluminum or pure aluminum either of which would require a heavier gage.
Top
#78131 - 08/21/01 03:41 PM Re: Stove outlet
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Todd,

It sounds like you are unfamiliar with this situation and would no doubt be better off with some help in this. I would suggest that you contact someone locally that is Licensed/Certified and capable of handling this. Everyone will sleep better at night.


Bill
Top
#78132 - 08/21/01 05:45 PM Re: Stove outlet
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
I would ask Kenmore if that could be a typo
Top
#78133 - 08/21/01 06:14 PM Re: Stove outlet
Anonymous
Unregistered

I think it just means pure copper rather than aluminum, steel, carbon, or anything else.
Top
#78134 - 08/21/01 06:58 PM Re: Stove outlet
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
Probably;
I'm not aware of any 8-3 solid in a cable
Top
#78135 - 08/21/01 07:19 PM Re: Stove outlet
Anonymous
Unregistered

8-3-G solid copper is not something I would want to have to unroll much less bend.
Top
#78136 - 08/22/01 07:59 AM Re: Stove outlet
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Stranded is fine.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#78137 - 08/22/01 08:03 AM Re: Stove outlet
Todd Offline
Junior Member
Registered: 08/21/01
Posts: 3
Loc: Cincinnati, Oh USA
Hmm... back to Home Depot I go! Good thing you can return cut wire there...

I didn't take distance into consideration when I read the owner's manual. Now that I think about it I know 6 will be a better choice. I am installing this into an 1950 house and the gap between the plaster and cinder block is only about an inch so I was worried about the wire being to big to install. I am going to install this in conduit because of this.

Although 8 on a 40 would have been safe... I don't want to be tripping breakers while trying to cook dinner.

Thanks for everyones advice!
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 105 Guests and 18 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals