ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,626 Are you busy
166,455 Re: Forum
160,717 Need opinion
Who's Online Now
0 registered members (), 68 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#78064 - 08/13/01 05:31 PM J-box grounding  
tmon  Offline
Member
Joined: Jul 2001
Posts: 29
I would like to know everyones opinion on the grounding of every switch, receptacle and junction box. Are you guys requiring and/or installing a grounding jumper from the equipment grounds to the box?


2017 / 2014 NEC & Related Books and Study Guides

#78065 - 08/13/01 06:55 PM Re: J-box grounding  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
My opinion tmon, is not necessarily code driven as much as liability driven.

I say ground it ALL, a small price to pay for some sound sleep.

Of interest, i believe 380-12 addressed more stingent grounding of switches in the 99' code cycle.

[Linked Image]


#78066 - 08/13/01 07:51 PM Re: J-box grounding  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Could you be more specific?
As far as j-boxes, I dont believe you have a choice if an EGC is run.(See 250-148)
Receptacles, the only other option is self-grounding receptacles.
As far as switches, see 380-9(b)


#78067 - 08/13/01 09:17 PM Re: J-box grounding  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Ground it, Ground it, Ground it.


#78068 - 08/19/01 09:15 AM Re: J-box grounding  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
250-148 (a) Says If you have a separate grounding conductor pulled in the box, it will be bonded to that box. Nuff said ?


#78069 - 08/19/01 09:20 AM Re: J-box grounding  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Shoot !!! another half answer, lemme do some more 'splainin' . Our specs at Dulles airport require that 1) You WILL pull an equipment grounding conductor, and 2) You WILL land it to any box it goes through - which, of course is very plain. Why ? you may ask.

In these days of cell phones, FRS radios, etc.. we find that RF has a nasty way of getting into and interfering with intricate systems. Also,Bill Summers stated several years ago that he wanted to see the practice of conduit bonding ended, then went into an expanation that convinced me thoroughly. There is the code, and a very quick reason.


#78070 - 08/21/01 05:56 PM Re: J-box grounding  
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
To the doubter's, I suggest looking at the 1995 Annual Meeting NATIONAL ELECTRICAL CODE REPORT on PROPOSALS ( ROP );

Log # 950
5 - 309 - (250-114 )

on page 249.

Glenn



Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7815 MB (Peak: 0.9324 MB) Zlib enabled. Server Time: 2017-03-28 06:21:41 UTC