The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
failed home inspection.
by HotLine1
01/19/17 01:41 PM
Safety at heights?
by Trumpy
01/19/17 05:25 AM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
1 registered (Ruben Rocha), 0 Guests and 197 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#78056 - 08/13/01 04:43 AM Portable cord sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I occasionally wire portable pumps with self-contained 3 ph. starters mounted on the unit. They are fed by plugging into 20 amp branch ckts. A typical size is 1.5 HP (3 amps @ 480 volt). Article 400-13(OC protection for the cords) refers to 240-4. 240-4(a) requires OC protection in accordance with the cords ampacity per table 400-5(A), which requires 12 gauge cord for 20 amps. However, 240-4 allows supplementary OC protection as in 241-10 to protect the cord. Is the OL relay in the starter considered to be this supplementary OC protection, and therefoe, can I use cord smaller than #12, based on OL heater size?

Top
2017 / 2014 NEC & Related Books and Study Guides
#78057 - 08/13/01 04:26 PM Re: Portable cord sizing
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Redsy;
I'm reading 430-6 The 2nd sentence refers to 400-5, and then ends up in the usual motor tables.
430-22 still applies
of interest,430-42(c) shows a 15 A 99' change

Top
#78058 - 08/13/01 05:13 PM Re: Portable cord sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Sparky,
Thanks. But I'm still hung up on supplementary OC protection as mentioned in 240-4(a). This would allow me to use 14/4 or even 16/4, instead of 12/4 to supply the starter. Remember, it's pulling less than 3 amps, so voltage drop shouldn't be much of a problem. If I can use smaller cable, I'd like to. We usually put about 35' of cord on the pump, and 12/4 can be a nuisance for the operators.

Top
#78059 - 08/13/01 06:15 PM Re: Portable cord sizing
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
ok,
210-4(a) does refer to 400-5.
240-9 would seem to side with you here.
I was looking for some reference in 430, to either code loop there or 'amend' the loop out.
I guess i'm still sittin' the fence here

Top
#78060 - 08/14/01 04:31 AM Re: Portable cord sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks, sparky.
I like 240-9. It was right in front of my eyes, but I didn't see it.

Top
#78061 - 08/14/01 04:17 PM Re: Portable cord sizing
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Well i've gone back and forth here, seems you got a winner.
Lemme play devil's advocate...
Suppose you had a setup with an adjustable setup, like those new Furnace jobs that can 'dial-in' what you need.
Per code that setting can be played with, so would we size to the upper limit of the range???

Top
#78062 - 08/14/01 05:40 PM Re: Portable cord sizing
Anonymous
Unregistered


> would we size to the upper limit of the range???
I should think so unless you can otherwise securely limit the maximum.

Top
#78063 - 08/14/01 07:06 PM Re: Portable cord sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Quote:
Originally posted by sparky:
Well i've gone back and forth here, seems you got a winner.
Lemme play devil's advocate...
Suppose you had a setup with an adjustable setup, like those new Furnace jobs that can 'dial-in' what you need.
Per code that setting can be played with, so would we size to the upper limit of the range???


I have 2 of those animals(Smart OL Relay?) on the shelf right now. Allen-Bradley, though. I'm home now, but I recall that even thuogh they are adjustable, you have to choose from a few different ranges for each size starter. This narrows it down somewhat. So, even adjusting all the way up, you won't be going very far for a given relay.