The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (Radar), 321 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77959 - 07/29/01 04:27 PM Track Trick
sparky Offline

Registered: 10/18/00
Posts: 5545
If I install 100' of track lighting, what should i feed it with?

2014 / 2011 NEC & Related Books and Study Guides
#77960 - 07/29/01 06:04 PM Re: Track Trick
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
220-12 (b) Track Lighting. For track lighting in other than dwelling units or guest rooms of hotels or motels, an additional load of 150 volt-amperes shall be included for every 2 ft (610 mm) of lighting track or fraction thereof.


The requirements of Section 220-12(b) previously appeared in Section 410-102 but they were moved to Article 220 for the 1999 Code since they deal primarily with load calculations.
Suppose a lighting plan shows 62.5 linear ft of single-circuit track lighting for a small department store featuring clothing. Since the actual track lighting fixtures are owner supplied, neither the quantity of track lighting fixtures or the lamp size are specified. What is the minimum calculated load associated with the track lighting that must be added to the service or feeder supplying this store?
According to Section 220-12(b), the minimum calculated load to be added to the service or feeder supplying this track light installation is calculated as follows:
62.5 ft ¸ 2 ft = 31.25 ft
31.25 must be rounded up to 32
32 ´ 150 VA = 4800 VA
4800 VA is the minimum load that must be added to the service or feeder calculation.
It is important to note that the branch circuits supplying this installation are covered in Section 410-101(b). For the track lighting branch-circuit load, the maximum load on the track cannot exceed the rating of the branch circuit supplying the track. Also, the track must be supplied by a branch circuit that has a rating not exceeding the rating of the track. The track length does not enter into the branch-circuit calculation.
Section 220-12(b) is not intended to limit the number of feet of track on a single branch circuit nor is it intended to limit the number of fixtures on an individual track. Rather, this section is intended to be used solely for load calculations of feeders and services.
Joe Tedesco, NEC Consultant

#77961 - 07/30/01 12:13 AM Re: Track Trick
sparky Offline

Registered: 10/18/00
Posts: 5545
would'nt you say 220-12(b) is a good 'guide' as the 'load' can be indiscriminatly changed easily?

tracks are not a 'fixed' load that do not change. 410-101(b) and 220-12(b) seem to almost conflict here read side by side.

could each head possibly fall under 220-3(b)(11) @ 180W per?

this just does not sit right.

[This message has been edited by sparky (edited 07-30-2001).]

#77962 - 08/07/01 08:34 AM Re: Track Trick
WARREN1 Offline

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
From a design standpoint, we have done this in the past:
Using Joe's example, we have 4800va divided by 120 v equals 40Amps divided by 16 (80% of 20) equals 2.5 circuits, rounded up to 3 with less than 16 amps each. That would be the minimum number of circuits required. Of course, more circuits would be better, however, realistically, only one or two fixtures per two foot length is how you will see track lighting. Most applications of the track lighting fixtures use 75-100 watt flood lamps or less. Higher ceilings may require the use of 150watt narrow beam lamps.
Just another thought.

#77963 - 08/07/01 05:25 PM Re: Track Trick
sparky Offline

Registered: 10/18/00
Posts: 5545
i would do the same.
my point is that , 220 not applying, i could run #14-2 to 100' of track if the owner wished for 3 heads.

the calc and reality seem to have a wide gap here.

and i don't care what anyone says....
it's IS NOT a fixed load!
only a ladder ( maybe) is required to install more heads.


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals