#77891 - 07/19/01 07:43 AM Article 645
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with
a ground conductor in it?

Joe Lusso, Electrical Plant Engineer
Facilities Project Management
303.673.5248 phone
303.673.4551 fax
email: LussoJA@louisville.stortek.com
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#77892 - 07/19/01 08:58 AM Re: Article 645
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Doesn't 645-5 (d) (2) permit rigid non-metallic (PVC) conduit?
Top
#77893 - 07/19/01 10:13 AM Re: Article 645
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Redsy:

Yes, and the question is really not very clear. I have invited the person who asked this question to come aboard here on theis BB and look for the help he needs. I always bring these types of question here so we can all put our thoughts into the discussion.
_________________________
Joe Tedesco, NEC Consultant
Top
#77894 - 08/05/01 09:33 AM Re: Article 645
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
Quote:
Originally posted by Joe Tedesco:
Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with
a ground conductor in it?


Most of the limitations on the use of PVC conduit inside buildings are the result of concerns about the fuel and smoke contributed under fire conditions rather than its performance as a raceway.
--
Tom
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals