ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
TRUE POWER
by jraef. 03/21/17 09:13 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,421 Are you busy
166,141 Re: Forum
160,595 Need opinion
Who's Online Now
1 registered members (ComputerWizKid), 51 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#7766 - 02/20/02 06:43 PM Commerical Kitchen  
Boomer  Offline
Junior Member
Joined: Feb 2002
Posts: 5
In a commerical kitchen when the fire suppression system in the range hood senses a fire and shuts off the gas valves, by the NEC should it also shut the power off to ranges & ovens under the hood? Boomer


Work Gear for Electricians and the Trades

#7767 - 02/20/02 09:16 PM Re: Commerical Kitchen  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Boomer,
It’s not an NEC requirement. I believe it is in the fire codes. Generally all power under the hood must shut down. Make up air must shut down and exhaust fans must turn on or continue to operate. Check with the local AHJ in your area as requirements vary from place to place.


#7768 - 02/21/02 09:59 AM Re: Commerical Kitchen  
Bob Hinshaw  Offline
Junior Member
Joined: Jan 2001
Posts: 5
Tipp City, Ohio, USA
Boomer,
A shunt trip circuit breaker should be installed through the fire panel at the hood.
All lights and especially the exhaust fans should be wired into them. When the fire systems is activated, it will shut power off to the range hood. There should be a wiring diagram in the fire panel for the proper wire connections.


#7769 - 02/21/02 06:00 PM Re: Commerical Kitchen  
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
I believe that NFPA allows exhaust fans to continue to run but any make up air must be shut down.

And I think this is a pretty new rule, maybe 95?


#7770 - 02/23/02 10:07 AM Re: Commerical Kitchen  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Although a shunt-trip breaker is an acceptable method, the circuits can be run through electrically held contactors controlled by the fire panel. The benefits are that you don't have to lose the extra breaker space required by the shunt c/b, no external power is required to operate the shunt in the event of the shunt's control circuit being turned off (which could go undetected), and $$$.



Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7655 MB (Peak: 0.9030 MB) Zlib enabled. Server Time: 2017-03-25 13:39:58 UTC