#7766 - 02/20/02 02:43 PM Commerical Kitchen
Boomer Offline
Junior Member
Registered: 02/16/02
Posts: 5
In a commerical kitchen when the fire suppression system in the range hood senses a fire and shuts off the gas valves, by the NEC should it also shut the power off to ranges & ovens under the hood? Boomer
Top
Work Gear for Electricians and the Trades
#7767 - 02/20/02 05:16 PM Re: Commerical Kitchen
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Boomer,
It’s not an NEC requirement. I believe it is in the fire codes. Generally all power under the hood must shut down. Make up air must shut down and exhaust fans must turn on or continue to operate. Check with the local AHJ in your area as requirements vary from place to place.
Top
#7768 - 02/21/02 05:59 AM Re: Commerical Kitchen
Bob Hinshaw Offline
Junior Member
Registered: 01/05/01
Posts: 5
Loc: Tipp City, Ohio, USA
Boomer,
A shunt trip circuit breaker should be installed through the fire panel at the hood.
All lights and especially the exhaust fans should be wired into them. When the fire systems is activated, it will shut power off to the range hood. There should be a wiring diagram in the fire panel for the proper wire connections.
Top
#7769 - 02/21/02 02:00 PM Re: Commerical Kitchen
maintenanceguy Offline
Member
Registered: 12/02/01
Posts: 300
Loc: Southern NJ, USA
I believe that NFPA allows exhaust fans to continue to run but any make up air must be shut down.

And I think this is a pretty new rule, maybe 95?
Top
#7770 - 02/23/02 06:07 AM Re: Commerical Kitchen
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Although a shunt-trip breaker is an acceptable method, the circuits can be run through electrically held contactors controlled by the fire panel. The benefits are that you don't have to lose the extra breaker space required by the shunt c/b, no external power is required to operate the shunt in the event of the shunt's control circuit being turned off (which could go undetected), and $$$.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals