In Mike Holts "Masters Electrician Prep Book", he refers to the 90 degree column in T310-16 and states that this column is used primarily for ampacity derating. Has anyone else read or heard this?
Top
2017 / 2014 NEC & Related Books and Study Guides
#77647 - 07/06/01 03:32 AM Re: Use of 90 degree rated cable
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Hi tmon,
yes , we are allowed to use the highest figure to start derating calc's from, i believe there was a code cycle to clear this up, but am at a loss this morning for an article...
Top
#77648 - 07/06/01 03:34 AM Re: Use of 90 degree rated cable
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
It's always been that way.

Most earier Circuit Breakers ( small size ) were rated for 60º terminations.

Now many are rated for 60/75º terminations.

Usually only high voltage systems and bus work is the only items rated for 90º terminations.

Look at the labeling within panels and on equipment terminal info.

Also NEC 110-14(c) must be followed. Although is has only been in the NEC the last few cycles, it has always been in 110-3(b) and the UL White book has had the info for many mnay years, usually with-in the first 8 pages of text.

Glenn
Top
#77649 - 07/07/01 04:50 AM Re: Use of 90 degree rated cable
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
thanks Glenn
Top
#77650 - 07/07/01 11:54 AM Re: Use of 90 degree rated cable
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
tmon,

Welcome to the group!!!

Just wanted to point out one of the more "simpler" points on using the 90 degree column for derating is the reason we can put upto 9 current carrying conductors [#12 THHN cu] in the same raceway, and still have them rated at 20 amp max.
What is being done here is the 30 amps maximum for #12 in the 90 degree column is used for the derating number - so for 9 current carrying conductors, 70% of 30 amps is 21 amps.

Scott SET.

Quote:
Originally posted by tmon:
In Mike Holts "Masters Electrician Prep Book", he refers to the 90 degree column in T310-16 and states that this column is used primarily for ampacity derating. Has anyone else read or heard this?
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals