#77641 - 06/29/01 06:58 PM 110-16 and 384-3 or 4
doc Offline
Member
Registered: 11/25/00
Posts: 119
Loc: Texas
I dont have my book so be kind here if im wrong on articles but 110 deals with clearance issues and 384 says that 25 ft above panels is to contain nothing but electric equipment,now do i understand that if u have a breaker panel or a panel board that u cannot run anything above it unless it is electrical we are running a steel conveyor about 8-10 ft above a 200 amp breaker panel
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Top
2017 / 2014 NEC & Related Books and Study Guides
#77642 - 06/30/01 03:26 AM Re: 110-16 and 384-3 or 4
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
doc;
110-26(f) mentions 384
110-26(f)(1)(a) EX, talks about foreign systems
which is defined in (b), as long as U provide protection from condensation,leaks or breaks your conveyor can stay.
Top
#77643 - 07/12/01 07:53 PM Re: 110-16 and 384-3 or 4
doc Offline
Member
Registered: 11/25/00
Posts: 119
Loc: Texas
sorry to be so long getting back but sparky would you take another look at these codes one talks about working area and the other is dedicated space and I see nothing about water it says nothing but electrical is allowed above it am i still missing something I have a book by Mike Holt understanding the code and it shows this area to be left open now what am i missing
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Top
#77644 - 07/12/01 07:59 PM Re: 110-16 and 384-3 or 4
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Doc,
I don't think you are missing anything. clear space is clear space, NOTHING goes above that panel except electrical equipment. The purpose was for the electrician to always have a path to the panel, conveyors would be in the way, sorry, in my jurisdiction, down it comes.
Top
#77645 - 07/12/01 09:39 PM Re: 110-16 and 384-3 or 4
Anonymous
Unregistered

How about if he just suspends a slab of concrete there so the conveyor is on the next floor up in the building?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals