The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77630 - 06/28/01 06:53 PM Metal or plastic Face plate

We are in a debate on what should, or should not be used. I was told that we must use a metal face plate for Garage GDO's, yet, another electrician told me that it doesn't matter. Which is correct. Note: It made logical since at one point to use the metal, to protect the wires in the GDO's recepticle-if a fire was to break loose. (located in the ceiling of the garage--does not need GFCI protection).

2014 / 2011 NEC & Related Books and Study Guides
#77631 - 06/29/01 04:44 AM Re: Metal or plastic Face plate
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
There is a requirement(although the std. escapes me right now. Joe?) that fire ratings must be maintained in the event of penetrations in fire rated walls(attached garages would apply). This includes disallowing back-to-back penetrations in the same stud cavity, limiting the total area of the wall space allowed for device boxes(100, and using metal boxes on fire-rated walls. If a metal box is required to maintain fire resistance ratings, a plastic plate seems to diminish its effectiveness.

#77632 - 06/29/01 05:08 AM Re: Metal or plastic Face plate
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
To properly maintain the fire rating of the ceiling, the box should be wrapped with an approved fire pad. If there was a requirement for metal plates, they would be required in all fire corridors, etc. Besides, why have a metal plate when the fire will burn right through the plastic device?

[This message has been edited by electure (edited 06-29-2001).]

#77633 - 06/29/01 09:12 AM Re: Metal or plastic Face plate
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Redsy: See the FPN,

Section 300-21. Spread of Fire or Products of Combustion

Electrical installations in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased.

Openings around electrical penetrations through fire-resistant-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.

FPN: Directories of electrical construction materials published by qualified testing laboratories contain many listing installation restrictions necessary to maintain the fire-resistive rating of assemblies where penetrations or openings are made.

An example is the 24-in. (610-mm) minimum horizontal separation that usually applies between boxes on opposite sides of the wall.

Assistance in complying with Section 300-21 can be found in these directories and product listings.
Joe Tedesco, NEC Consultant

#77634 - 06/29/01 04:01 PM Re: Metal or plastic Face plate
njelectricmaster Offline

Registered: 04/29/01
Posts: 110
Loc: Lead, South Dakota
Hello From Colorado!!!!!!!

I have noticed on the inside of the plastic boxes that I use, The single gang boxes are rated for 2 hour fire and the 3/0 light boxes are rated for 4 hour fire.

We are required to use only 4 hour fire rated boxes in the cielings.

Any one else???????
Jon Niemeyer

#77635 - 06/29/01 04:28 PM Re: Metal or plastic Face plate
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Allied makes 1 & 2 gang fiberglass boxes that are 2 hour rated, can be in the same stud space & don't need putty pads. I don't think a metal faceplate is part of the fire rating on any box.

Few things are harder to put up with than the annoyance of a good example.

#77636 - 06/29/01 06:19 PM Re: Metal or plastic Face plate
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I must apologize. I was thinking in terms of metal boxes, which have holes in them.

[This message has been edited by electure (edited 06-29-2001).]