The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Radar), 326 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77546 - 06/20/01 07:19 PM UFER ?
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
In 2 cities right next to each other, Ufers are required to be installed in 2 different ways. One inspector wants the Cu tie wired right to the rebar. The other wants the Cu totally away from the rebar in the footing, but bonded together above the slab. Up until now I just have tried to remember which guy's city I'm working in.
Who's right???

[This message has been edited by electure (edited 06-20-2001).]

2014 / 2011 NEC & Related Books and Study Guides
#77547 - 06/20/01 07:53 PM Re: UFER ?

I think Ufer himself allowed the copper to be under the concrete. But in a wet area, the copper could possibly corrode away.

The place that is right is the one that requires a stainless steel rod to be welded to the rebar and left sticking out for the purpose of attaching the copper GEC.

#77548 - 06/21/01 03:31 AM Re: UFER ?
sparky Offline

Registered: 10/18/00
Posts: 5545
what is the rationale? is the voltage gradient affected either way?

#77549 - 06/21/01 10:25 AM Re: UFER ?
WARREN1 Offline

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
Searched "Ufer" and got an article published by Chris Scott in December of 1989 in Radio World magazine. According to the article, Mr. Ufer's findings were published in IEEE Transaction paper #63-1505.
"After much research and testing Mr. Ufer advised the Army to make connection to the steel bar that would internally reinforce the concrete foundation. He had determined that concrete was more conductive than all but the best soil, and that this improved semiconducting characteristic would enhance surface area contact with the surrounding soil. The wire ties normally used would be extra secure, and attention would be given to bonding or welding the lattice- type network together." We use this type system often doing design. The cage is wired together and a piece of CU is brought out to the steel column. This is all tied to the building ground loop, etc, to have a better than adequate grounding system.