The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#77522 - 06/20/01 07:00 PM Another Hot Tub problem
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
A "money is no worry" customer doesn't want a gaudy disconnect mussing up his view whilst enjoying his hot tub. It will be installed in a screened-in porch.

680-12 states that "...A disconnecting means shall be provided and be accessible, located within sight from all pools, spas and hot tub equipment..."

100-A says that "Disconnecting Means. A device, or group of devices or other means by which the conductors of a circuit can be disconnected from their source of supply."


My idea, not yet suggested to the customer, is perhaps to install a 15A SP switch that controls a contactor (50A) that switches the supplied power. (The switch will be in a WP box and cover). I believe my customer would be willing to pay the extra for the unspoiled view, and I'll go along as long as I'm not breaking code doing it.

Are 50A 2 Pole contactors available and are they rated for any type load, other that motors? (They're rated higher for non-motor loads, aren't they?)

Any problems with this idea?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
2014 / 2011 NEC & Related Books and Study Guides
#77523 - 06/20/01 07:35 PM Re: Another Hot Tub problem
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I'm not around any of my books right now, but 60 amp rated contactors are easily gotten; not sure on 50. Will you have to put a lockable cover on your switch?

Top
#77524 - 06/20/01 07:52 PM Re: Another Hot Tub problem
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
60A contactor would be fine... I should have said at least 50A..

As far as the lockable cover for the switch, for LOTO purposes? This is a residential situation, any difference there? Can the LOTO be used for the panel breaker instead?

_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#77525 - 06/20/01 08:01 PM Re: Another Hot Tub problem
Anonymous
Unregistered


I am pretty cold to that idea. I would not trust the contactor to disengage and remain disengaged. To me a disconnect is a manual switch on the circuit itself.

I could say, hey, browse to www disconnects.net and uncheck the box for your circuit and my computer will de-energize and lock it out for you.


Yeah, perhaps in a hundred years.

But I think a disconnect is a switch that I physically open and lock open, not some remote control button.


Now don't get me wrong, and emergency switch like this is okay. But if the in sight disconnect is for me to work on it, I want to see that the contacts are physically open.

Was that Scott who once shut down a power plant by accidentally shorting a control wire?

Top
#77526 - 06/20/01 08:21 PM Re: Another Hot Tub problem
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I would, personally, shut off the breaker in the panel before working on the hot tub, and I would not rely on a contactor to cut off the circuit for maintenance purposes either...

I suppose I assumed that the intentions of 680-12 is to provide a means of shutting down the hot tub for the "consumers", not entirely unlike an E-switch; although 680-38 gives exception for residential for actual E-switches.

The switch will not even remotely resemble a disconnect, so I see no danger for confusion where a maintenance shut off is required. I would bet that any maintenance man would shut-off the 50A GFCI breaker marked "Hot Tub" in the panel and not even notice the lowly switch on the wall.

This is simply my opinion, and any NEC quotes to thwart this idea will render this idea as useless.

Dspark, your good points and opinion has not gone unnoticed, however.
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#77527 - 06/20/01 10:35 PM Re: Another Hot Tub problem
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Virgil,

As far as I know, the main purpose of the disconnect within sight is to protect the repairman. They can turn it off and because it is within sight, can watch to make sure that no one turns it back on. In the past I've been able to avoid the "within sight" requirement (for the same reasons) if it is capable of being locked in the open position. Why don't you pass it by your AHJ.

Bill

Top
#77528 - 06/21/01 03:34 AM Re: Another Hot Tub problem
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
can the 'within sight' clause consider you moving said disco up to 50' away ?

Top
#77529 - 06/21/01 03:38 AM Re: Another Hot Tub problem
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
ya know, this brings another point to mind, no one likes to see our work! carpenters build stuff , everyone says OOOH!, we build stuff and they think it's ugly!

well i think my craft looks good!

( insert french accent here)

I am an arrrtissst!, I canno' wok likea dissss!


Top
#77530 - 06/21/01 04:30 AM Re: Another Hot Tub problem
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Could you mount the disconnect on the unit on the opposite(yard) side of the home. It wouldn't spoil his view because he won't be able to see it.

Top
#77531 - 06/21/01 04:33 AM Re: Another Hot Tub problem
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I don't think I've ever seen a contactor close on its own without some power being applied to the coil. Anyone working on the spa should check for live wires whether they have a disco or not. Wouldn't this be something like the EPO switch in a gas station, which shuts the power down to the turbine pumps?

Top