The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 281 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77500 - 06/16/01 06:50 PM Shunt-Trip Breakers
Webmaster Offline


Registered: 10/07/00
Posts: 3142
Loc: NY, USA
Posted for Matt:

what are the purposes for a shunt-trip breaker in a commercial range exhaust fan system? are there other ways to shut down the make up air in the case of fire which are acceptable by code.?

2014 / 2011 NEC & Related Books and Study Guides
#77501 - 06/17/01 09:59 AM Re: Shunt-Trip Breakers
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The shunt-trip C/Bs for a range hood are meant to shut down the electrical supply to anything under the hood and the air handling for the hood in case of a fire. Generally, there is a contact in the fire suppression system that will CLOSE when the temperature threshold is reached, which will energize the shunt (really no more than a magnetic solenoid) in the C/B and open the circuit. If it's acceptable to the AHJ, this can also be accomplished by routing your circuits through an electrically held contactor which will be controlled by a contact that will OPEN when the temp is reached. This is usually easier,it takes up less breaker space, and doesn't rely on the power to the controls being on to shut the system down.
Another method that can be used if you just have to control a motor that has a mag starter is to run the control circuit for the mag through the temp contact so it will open upon the sensing of the fire.

[This message has been edited by electure (edited 06-17-2001).]

#77502 - 06/17/01 07:36 PM Re: Shunt-Trip Breakers
golf junkie Offline

Registered: 04/22/01
Posts: 511
Loc: York, NE

I have not run into a shunt trip used for fan shutdown. We use them for elevator service when the elevator shaft is sprinkled.

All the fan shutdowns I have seen are wired into the fan controls. It would certainly do the job, though.


#77503 - 06/18/01 06:06 AM Re: Shunt-Trip Breakers
WARREN1 Offline

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
In addition to what electure has to say, some municipalities may require this system to be tied into the fire protection circuits which may inform local fire departments of a fire.