#77491 - 06/15/01 07:46 AM Medical Trailor
cinkerf Offline
Member
Registered: 12/03/00
Posts: 84
Loc: Pittsburgh, Pennsysvania. ...
A medical trailor is going to be transported to our Firefighters Training Academy. It will be used for testing for 4 days and then taken away. It will come equipped with a 60 amp. 120/240V. 60A. 4W. power cable and attachment cap. A 4W. receptacle will be installed near a subpanel to provide power. Is a ground rod required?

Frank (cinkerf)
Top
2017 / 2014 NEC & Related Books and Study Guides
#77492 - 06/15/01 09:43 AM Re: Medical Trailor
Mike Offline
Member
Registered: 02/21/01
Posts: 62
Does the medical trailer have a panelboard?
If it does have a panelboard then I would consider it a structure. Which would lead to Article 250-32, etc., requiring a ground rod. If it doesn't, then I would consider the trailer as portable equipment. Which wouldn't require a ground rod.

[This message has been edited by Mike (edited 06-15-2001).]
Top
#77493 - 06/15/01 10:37 AM Re: Medical Trailor
Anonymous
Unregistered

The metal shell of the trailer must throughly and solidly bonded to the EGC. You should test the resistance and find it to be low (<2 ohms). If it isn't bonded properly, then I see the need to get it correctly bonded. I don't see the need for a ground rod. A ground rod doesn't make a dangerous trailer safer.

I'm also assuming that the trailer will have a steel jack that would provide a path to earth if lightning strikes the trailer.
The trailer really should have metallic contact with the earth for lightning.

I'm assuming that the trailer has a panelboard - but I still consider it portable as evidenced by the fact that it will be rolled away after only 4 days.
Top
#77494 - 06/15/01 02:24 PM Re: Medical Trailor
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
hmmmm;
we need to become definitional here,

is this a structure ??

is this a mobile home???

is this a camper??

Top
#77495 - 06/15/01 04:07 PM Re: Medical Trailor
cinkerf Offline
Member
Registered: 12/03/00
Posts: 84
Loc: Pittsburgh, Pennsysvania. ...
The Medical Trailor does have a panelboard.

Frank (cinkerf)
Top
#77496 - 06/15/01 04:54 PM Re: Medical Trailor
Anonymous
Unregistered

It's not a structure mainly because it is not erected on site. Yes, a camper could be a good comparison. But I suspect that no one cooks or sleeps in this trailer.
Top
#77497 - 06/15/01 07:18 PM Re: Medical Trailor
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
to G-rod or not to G-rod , that is the Q.
hmmm;

550-23(a), last sentence refers to 250-32, so does this mean only the disco gets the rod?

while we are on it, what about art 553 , floating buildings ???
Top
#77498 - 06/18/01 05:41 AM Re: Medical Trailor
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
I would consider the trailer as portable equipment since it has a cord and attachment plug. Even though the trailer was probably manufactured to the stringent standards of MHMA and other required standards (which by the way are now a lot stricter than they were twenty and thirty years ago when I bought my first mobile home).
The cord and plug have two phase conductors, a neutral and a ground. The receptacle supplying power to the unit is deemed as grounded and providing a ground return path. Having said all of that, I think I would insure the shell and frame are electrically connected to the ground in the cable. An ohmmeter check should suffice. If your meter is in the truck a couple of hundred feet away then a scrap piece of #10 connected to the frame and to the receptacle conduit should provide a suitable ground path for fault currents. A separate ground rod may set up a situation with circulating ground currents, and may cause additional problems.
Top
#77499 - 06/18/01 07:19 AM Re: Medical Trailor
Mike Offline
Member
Registered: 02/21/01
Posts: 62
Read the thread "Carnival Tent" in IAEI BB. It doesn't matter what NEC article we "think" the medical trailer falls under. It's the AHJ's interpretation that counts
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals