The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77468 - 06/07/01 09:04 AM Quadplex Size for 200A
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
What size quadplex should be used for an overhead line for 200 A. ? Table 310-17 says 1/0 for 90ºC wire if it qualifies, and that seems to be the size that the PoCo uses.

This is for a dairy barn on the load side of the disco.

Also, the pole that will have the tap is only triplex, Bond the Neutral and Ground at the pole where the tap is made, or? It may be upgraded in the future.

Thanks

-Virgil
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
2014 / 2011 NEC & Related Books and Study Guides
#77469 - 06/07/01 12:17 PM Re: Quadplex Size for 200A
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
It seems that you are on the money if the terminals are rated for 90C. How long of a span is it? Around Phila., aerial PECO spans are usually only #4 al. even on 200A services. I used #6 quadplex for an overhead span of about 75' once, and as I was pulling it into the wedge clamp, it got pretty heavy. Have you ever used such large quadplex before? Is the pole the service point? Couldn't you bond in the disconnect?

Top
#77470 - 06/07/01 02:15 PM Re: Quadplex Size for 200A
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
hmmm,
a quick check of the good book,,,

as far as the MBJ, check out 250-30 , especially EX # 1.

sizing- 215-2 ( ampacity)

225-6 ( size)

547-8(c) i beleive throws out 250-32(b)(2) if i'm reading it right.


also why 310-17? does 310-20 look any better?




[This message has been edited by sparky (edited 06-07-2001).]

Top
#77471 - 06/17/01 06:26 AM Re: Quadplex Size for 200A
cinkerf Offline
Member

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
I think Table 310.16 would have to be used for quadruplex cable. I'm really not 100 percent certain. Table 310.17 is for single conductors. Table 310.16 would require 4/0 conductors if the terminals at the disconnect and the main breaker in the panelboard in the dairy barn are rated for 90 deg. In the area where I live it is not unusual for the Power Company to install triplex or quadruplex service drop conductors of a smaller size than the Contractors service conductors. They are not required to comply with the NEC for such an installation. However, for feeder conductors whether indoors or outdoors Table 310.16 should be used. Just my opinion....


Frank (cinkerf)

Top
#77472 - 06/17/01 07:48 AM Re: Quadplex Size for 200A
cinkerf Offline
Member

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
I will address this part of your post: Also, the pole that will have the tap is only triplex, Bond the Neutral and Ground at the pole where the tap is made, or? It may be upgraded in the future.

I would ground and bond at the pole. You are running a quadruplex cable to the dairy barn panelboard. Isolate the neutral in the panel, drive a ground rod and connect to the "fourth" wire. Also bond any copper water lines that may exist.
What do you think?

Frank (cinkerf)

Top
#77473 - 06/17/01 08:17 AM Re: Quadplex Size for 200A
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
That was the plan, wanted to know if it was the right plan though!

Thanks!

-Virgil
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#77474 - 06/17/01 09:41 AM Re: Quadplex Size for 200A
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Hey Virgil,
Do you have more pics for Photos/Discussion?
I really enjoy yours. You're the only one around that can catch 250+ violations in 1 photo!...scott

Top
#77475 - 06/17/01 03:24 PM Re: Quadplex Size for 200A
cinkerf Offline
Member

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
I feel that it is in compliance with the NEC