#7734 - 02/20/02 06:01 AM 10 amp circuit breakers
Bob Hinshaw Offline
Junior Member
Registered: 01/05/01
Posts: 5
Loc: Tipp City, Ohio, USA
I have a friend who was asking me about a problem he is having in his house. He keeps tripping 10 amp circuit breakers, especially on the freezer and micro wave circuit. First, I didn't know it was acceptable, especially in a newer home, to use 10 amp breakers. I cannot find in the code where it states that you can and what wire size to use. Is this acceptable, or should the breakers be changed, if the wire size is correct?
Top
Work Gear for Electricians and the Trades
#7735 - 02/20/02 08:51 AM Re: 10 amp circuit breakers
CTwireman Offline
Member
Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
10 amp breakers? That's a new one on me!! Could you give us some more information? Like the manufacturer and model # of the breakers and panel?

Are you sure that the writing hasnt worn off on the breaker and you are misreading it?
_________________________
Peter
Top
#7736 - 02/20/02 09:00 AM Re: 10 amp circuit breakers
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I believe some manufacturers make "unit breakers" to be individually mounted on a din rail or similar application, to protect specific piece of equipment. However, for branch ckts., 210.3 shows a minimum rating of 15 amps. Also, I don't believe UL lists branch circuit breakers below 15 amps

[This message has been edited by Redsy (edited 02-20-2002).]
Top
#7737 - 02/20/02 09:50 AM Re: 10 amp circuit breakers
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
You are right Redsy. Square D makes a QOU unit mount miniature breaker as low as 10 amps in 120/240 volts 1,2,3poles and 277 volts 1pole.
Art. 240-6 of the 1999 NEC list only as low as 15 amps, but the next sentence says non-standard fuses and inverse time breakers shall be permitted.
Top
#7738 - 02/20/02 09:50 AM Re: 10 amp circuit breakers
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
Square D and other breakers have a large #10 on the face, which means 10,000 Amps Interrupting Current, not 10A Overcurrent protection.

Look closer at the black numbers on the toggle itself if Sq D, or near there...

It should say either 15, 20, (or God forbid) 30 on it...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#7739 - 02/20/02 11:09 AM Re: 10 amp circuit breakers
Bob Hinshaw Offline
Junior Member
Registered: 01/05/01
Posts: 5
Loc: Tipp City, Ohio, USA
Thank you guys for your quick response to my inquiry. I have sent these responses to my friend who is going to double check his panel tonight. I am hoping it is what sparky66wv suggested. Will keep everyone posted.
Top
#7740 - 02/21/02 05:51 AM Re: 10 amp circuit breakers
Bob Hinshaw Offline
Junior Member
Registered: 01/05/01
Posts: 5
Loc: Tipp City, Ohio, USA
After further investigation, he discovered it was a 15 amp circuit breaker, with the large #10 on it. Well, he still has a problem, but I feel better. Thank you guys for your help.
Top
#7741 - 02/21/02 05:53 AM Re: 10 amp circuit breakers
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
10 amp breakers are common in industrial control panels. Square D makes a QO plug-on and QOB bolt-on panel style in 1, 2, and 3 pole versions as well as their unit mount QOU. (Look at page 8-10 in their Digest).

These are not common in normal panels or loadcenters.
Top
#7742 - 02/21/02 07:20 AM Re: 10 amp circuit breakers
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Bob,

Does He have a Microwave over the Stove?
Just a guess, because Kitchen receptacles should be on 20A circits. A common situation I've seen is for someone to replace a range hood (which is on a 15A general purpose circuit with multiple other loads) with a Microwave unit. It should have been put on a dedicated circuit.

Bill
Top
#7743 - 02/21/02 07:21 AM Re: 10 amp circuit breakers
CTwireman Offline
Member
Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Bob-
Youre Welcome. I suggest having an elctrician come take a look at that situation. It is possible that the #10 does not run throughout the entire ciruit, which would make it dangerous to upgrade the breaker to a 20 amp or 30 amp. Someone could have tapped #12 or #14 off of it, seeing that #10 is cumbersome to work with. At any rate, I would suggest professional assistance.
_________________________
Peter
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals