#77308 - 05/19/01 09:24 PM Derating and adjustment factors
doc Offline
Member
Registered: 11/25/00
Posts: 119
Loc: Texas
lets say u are running 440 volt 3 phase equipment.now inside conduit u run 21 wires all thhn #12 stranded these wires are going to 440 volt 3 phase motors do they get derated just like any other wire and if you get to a j-box and cut them into u now have 42 wires in that box would u then use a different derating # or would u still stay with 21 article 310-8{a} hope this makes since to u guys
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Top
2017 / 2014 NEC & Related Books and Study Guides
#77309 - 05/20/01 02:14 PM Re: Derating and adjustment factors
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
doc,
is there a NEC reason to not derate? and why 310-8(a) , i'm a little slow, sorry.....
Top
#77310 - 05/20/01 06:16 PM Re: Derating and adjustment factors
doc Offline
Member
Registered: 11/25/00
Posts: 119
Loc: Texas
SORRY FOR THE MIX UP I am looking in article 310 and in the 96 code book on page 196 u have 8 Adjustment factors then u have {a} at that point it shows 21-30 wires if I have 21 then I would derate them to 45 percent.Now i go to a junction box i cut them into at that point I now hve 42 wires in the j-box would I derate those wires using 41 or more which would be 35 percent or even though I did cut them in the j-box it would still be 21 wires hope this helps
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Top
#77311 - 05/20/01 06:42 PM Re: Derating and adjustment factors
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
oh, ok,,,
the 'pipe fill' bears derating,
30A(T310-16) x 45%(T310-15(b)(2))= 13.5A,
so next 240-6 would be 15A

the 'jb' needs only to meet fill requirements. As the wires have been cut, instead of passing thru, i beleive your fill requirements are doubled.
21 x 2.25= 47+ cubes
42 x 2.25= 94.5 cubes

ok doc?
Top
#77312 - 05/20/01 10:15 PM Re: Derating and adjustment factors
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
doc,
Derate like this:

Table 310-16: #12 THHN cu @ 90 degrees = 30 amps.
Table 310-15(b)(2)(a): Number of current carrying conductors: 21-30 = 45%
Multiply 30 amps x .45 = 13.5 Amps

This is for 30 degrees C Ambient Temperature. If higher than 30 C, adjust maximum amperage of 310-16 [30 amps for #12 THHN cu] by the corection factor, then derate for 21-30 conductors.
If the loads are LCL, then derate the maximum amperage [30 amps for #12 THHN cu] by 80%, making it 24 amps - then apply temperature corrections [if any], then finally derate for 21-30 current carrying conductors.

The conductors in the raceway [conduit] are the ones being derated. Box fill is another area.

Steve had already pointed out the corrected value of 13.5 amps - using 15 amp OCPD, so this message is just to explain how he came up with that figure.

Scott SET
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#77313 - 05/21/01 03:52 AM Re: Derating and adjustment factors
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
ok guys...
that's the normal routine.
doc's got motor circuits here, so let's apply 430, part D if branch circuits, part F if control circuits

which have you doc?
Top
#77314 - 05/21/01 05:49 AM Re: Derating and adjustment factors
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Guys,
Remember that with motor circuits the dreated ampacity of the conductors only has to equal 125% of the motor current as shown in Tables 430-147 through 430-150. It does not have to equal the rating of the branch circuit short-circuit and ground fault protection device.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#77315 - 05/21/01 02:18 PM Re: Derating and adjustment factors
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Another reminder that doesn't apply to this post, but seems to be a common oversight, you cannot round up to 15 amps if the conductors are part of a multi-outlet branch circuit that supplies receptacles for cord and plug connected portable loads.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals