#77271 - 05/19/01 05:23 AM Cable Trays
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
given a 24" cable tray that contains only 500mcm stacked in layers what is the violation there?

twelve 500mcm cables are distributed across the bottom of the tray...ladder type...on top of those is another layer.

as i read the code it doesnt allow for this.

given the addition of multi-conductor cables it gets even more restrictive.

thanks for any input
Top
2017 / 2014 NEC & Related Books and Study Guides
#77272 - 05/19/01 06:24 PM Re: Cable Trays
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
OK Frodo,
I'm bored and no one else has answered, I'll bite.

318-10(1) seems clear with no provisions for exceptions.

Single conductor cables, 2000v or less,

(1) Where all cables are 1000kcmil or larger, the sum of the diameters shall not exceed the cable tray width.

GJ
Top
#77273 - 05/19/01 06:29 PM Re: Cable Trays
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
If the voltage is over 2kv, (this is a powerhouse, right?)
then 318-12 and 318-13 are even more restrictive.
Top
#77274 - 05/19/01 06:32 PM Re: Cable Trays
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
It's Saturday night and I'm digging thru the NEC and posting at ECN........

man, I gotta' get a life.
Top
#77275 - 05/19/01 07:31 PM Re: Cable Trays
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
Quote:
Originally posted by golf junkie:
It's Saturday night and I'm digging thru the NEC and posting at ECN........

man, I gotta' get a life.


yeah its sat night and being away from home is about as bad...

yes it is a powerhouse...but the voltage is 480vac...

the contractor is not even attempting to follow the nec on the job...

there are a lot of violations around....this is one that i really wanted to be sure on so i figured i would ask for some opinions..they have stacked a couple layers of 500MCM conductors in a 24" tray and i think they are planning on dumping some control cables in there as well as some multi-conductor power cables...3/C 12, etc...

ge requires that the nec be followed if it is on our equipment even if it is a powerhouse...i have never seen a job where the nec was not recognized..

pictures available

thanks for the input
Top
#77276 - 05/19/01 08:10 PM Re: Cable Trays
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
Quote:
Originally posted by golf junkie:
OK Frodo,
I'm bored and no one else has answered, I'll bite.

318-10(1) seems clear with no provisions for exceptions.

Single conductor cables, 2000v or less,

(1) Where all cables are 1000kcmil or larger, the sum of the diameters shall not exceed the cable tray width.

GJ


don't you mean 318-10 (2) 500mcm are smaller than 1000kcmil i thought?

i was thinking 318-8, 9 & 10 covered it pretty well, indicating that you can not stack single conductors except for grouping?
Top
#77277 - 05/19/01 08:35 PM Re: Cable Trays
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
Frodo,
You're right....
I had confused the conductor size with your post on seal offs.

My bad.

GJ
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals